GBDamo

-
Supporter
Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:  American Electrical Advice Forum

After the YY burnout posted in;-



I intend to rewire and have given a rough quote.

Background.

These lights are head height wall mounted intended to illuminate the engine bay of a car, 10 workstations in a large workshop.

At present they are through wired through each other so, if the cable goes in one they all go upstream.

The reasoning behind my intention is that should one fitting go then the a fuse will blow highlighting the damaged fitting and allow continuity of works with the other lights.

Also allows for the damaged light to be worked on without isolating the circuit (FCU option).

Intention

Is to re-wire in galv conduit in 2.5 singles running the whole circuit off a c25 MCB.

And

1, give each fitting it's own FCU fused to 3A

or (see Questions)

2, Fit a 5x20mm fuse holder to an IP65 JB and use a quick blow fuse.

Then flex down to each fitting from the FCU/JB.

The customer is keen on this approach if it is reasonably feasable.

Questions

1, I can't find a source I trust for a 3A BS1362 curve, BBB don't have it so can't be sure the BS1362 will go before the MCB, any pointers?

If the above is a non starter;-

2, Does anyone see an issue with the approach of fitting fuse holder to a JB and 5A F rated fuse, this route also allows me to down rate the circuit CSA and MCB and ?
 
Last edited:
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members
Advertisement - Content continues below

ipf

-
Mentor
Arms
Esteemed
I'm not really with you there.
I wouldn't think they're wired in series, though.

edit. Just install led's fed from a 6amp mcb. If one's faulty, why would it affect the rest, unless it's a wiring fault or fitting short?
 
Last edited:

telectrix

-
Mentor
Arms
Esteemed
think they are in parallel, but if 1 goes tits up ( fried ballast is fav.) it takes out the MCB for all.
 
They will be wired 'daisy chain' fashion not in series but an earth leakage fault could still take the lot out (if protected by a RCD!)
Sounds like quite an expensive job!
 
T

The Ghost

Don't the fittings already have a fuse in them they usually do.
 
I think you are over engineering this. Would make more sense maybe to have two circuits across alternate fittings. Why a 25A, type C.
 

GBDamo

-
Supporter
  • Thread Starter Thread Starter
  • #10
The few I've see seem to be on the PL in emergency fittings.

These are not internally fused.
 

GBDamo

-
Supporter
  • Thread Starter Thread Starter
  • #11
I think you are over engineering this. Would make more sense maybe to have two circuits across alternate fittings. Why a 25A, type C.
Looking to make sure the BS1362 blow first, VD means the singles will be 2.5mm.
 

ipf

-
Mentor
Arms
Esteemed
They will be wired 'daisy chain' fashion not in series but an earth leakage fault could still take the lot out (if protected by a RCD!)
Sounds like quite an expensive job!
Why expensive? Just replace the fittings and feed from plug in roses so that you can isolate any faulty ones.
 

ruston

-
Mentor
Arms
Esteemed
Advent Win
And as has been suggested go for LED's , they will pay for themselves in no time .
 

GBDamo

-
Supporter
  • Thread Starter Thread Starter
  • #15
And as has been suggested go for LED's , they will pay for themselves in no time .
They still need a circuit running in as the YY is fried, due to the environment it needs to be in galv.

Adding tend LED non corrosives to the bill would be a no go.
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Ten 6ft fluorescents in a line in the Electrical Forum area at ElectriciansForums.net

Aico 3000 Range
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom