Morning all,
When terminating armoured into a Cu on the outside of the casing I.e sides, top, bottom, we use a gland this is straight forward but what if the cable comes into the back of the Cu how do you terminate safely and sturdy it in that case? Surely thru a grommet with relevant fire proofing isn’t enough incase cable/s are yanked on or pulled from the other side if coming in from an outside wall for example.
thanks in advance for any help and tips...
 
Get a steel adaptable conduit box. Remove lid and bolt the box to the rear of the consumer unit using the lid fixing points. Gland cable to box and bring in cable to the rear of the consumer unit.
 
or..... sink a knocout box into wall behind CU use rear knockouts to gland cable with a pirhana nut. tails into CU, nor forgetting fly lead for earthing.
 
At the first fix stage you terminate it into a metal box which is flush in the wall.

If its going into an existing stud wall you can fit the gland to an inspection elbow and bush that onto the back of the CU.
 
Morning all,
When terminating armoured into a Cu on the outside of the casing I.e sides, top, bottom, we use a gland this is straight forward but what if the cable comes into the back of the Cu how do you terminate safely and sturdy it in that case? Surely thru a grommet with relevant fire proofing isn’t enough incase cable/s are yanked on or pulled from the other side if coming in from an outside wall for example.
thanks in advance for any help and tips...
Or >>> Fix a 1 or 2 way metal Switch fuse unit along side the existing consumer unit specifically for the SWA cable.
 

Reply to Terminating armoured... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have a slightly odd requirement that means I am wanting to route a 3 core 4mm SWA cable (14mm outside diameter) from outside through a cavity...
Replies
3
Views
5K
Hi I have been in the electrical contracting industry all my working life 40 years and became a member of the NICEIC in 2006. During this time I...
Replies
17
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
I have installed outside socket by spuring of a socket from inside the house..(straight off the back of it. No distance). I am now wanting to put...
Replies
3
Views
1K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock