Hey all,

I'm playing with my new Metrel mi3000 and using my parents house as a quinea pig.

So if you see in the pic it has the main/rcd switch as a cutout and when trying to measure the zs my little Metrel trips it every time (tried on non trip and normal).

I have my R1+R2 and ze so can calculate zs but would just like your thoughts.

When I did an Rcd test at 100ma it trips at 28ms.



test & inspect tripping when doing zs on not trip {filename} | ElectriciansForums.net
 
You get the odd one that will trip every time on a 'no trip' test....I had one yesterday. Might be a sign that there is excessive earth leakage due to a low IR,or a 'tired' RCD,or just one of those things that you just have to accept and move on.
 
Spartykus I did not disconnect the rest of the house. I've probably done something wrong but didnt believe everything else have to be disconnected?

thanks in advance.
 
If you have all the house circuits live when you are testing Zs on no trip setting then if there is already about 90mA leakage from the existing installation the additional current that the tester uses would push the RCD into tripping.

Have you tested the RCD for the current at which it trips (ramp test) it may be that it is tripping at, say, 55 mA instead of the 100mA.
 
...Too slow again...as^^,try testing the RCD fully disconnected,to give a true value of its' tripping current,then,move on to find out what,if anything,is adding to its' threshold. Top-marks to playing with your device in order to get familiar with it. It will be those hours that enable you to use confidently,and interpret results effectively.As a kid,my folks sat around in the dark a lot during my frequent "safety tests"...:stooge_curly:
 
Hi junior-sparky

sorry for delay in replying but nothing to add as Mr Burns /PEG have said the required words
 
Hello All,

i was doing this using the 3 pin plug adaptor.

i had a little play again today and the RCD tripped at 110ma again at 28ms, well it said 110ma.


another question please... As I'm having issues getting a measured zs i calculated it. Ring final for whole house.

R1 0.50
R2 084
ze 0.10

zs total - 1.44 not good.

These are type 2 bs 3871 push fuses and max zs is 0.87 using the rule of thunmb.

I'm still learning but i know this is not good, would increasing the main earthing from the 6mm to 16mm make the difference or am i way off the right trail?

thank you
 
...Too slow again...as^^,try testing the RCD fully disconnected,to give a true value of its' tripping current,then,move on to find out what,if anything,is adding to its' threshold. Top-marks to playing with your device in order to get familiar with it. It will be those hours that enable you to use confidently,and interpret results effectively.As a kid,my folks sat around in the dark a lot during my frequent "safety tests"...:stooge_curly:


look after your tools they look after you, and play of course.
 
Are 0.5 and 0.84 your end to end readings for your ring final conductors ?
If so then these are your r1 and r2, and you need to look up again how you obtain R1+R2 for a ring final.
 

Reply to test & inspect tripping when doing zs on not trip in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock