Hi All,

Im new to this site and this is my first post.


Can someone give me advice on doing a fault loop impendence test on a 3 phase motor?
 
I presume you are checking for earth loop at the motor connection itself?
Take the connection cover off and clip one lead in to the earth terminal, one to the neutral terminal and then test to each phase in turn. You need to take all readings.
I'm not sure if this sounds like I'm taking the mick but it is that simple unless I've misunderstood.
 
Yes, the 3 phase motor would not be connected if you were doing an EFLI. You are testing the circuit not the appliance.
Do as johnboy6083 said Zs at isolator plus R1+R2 from isolator to motor connections.
 
I presume you are checking for earth loop at the motor connection itself?
Take the connection cover off and clip one lead in to the earth terminal, one to the neutral terminal and then test to each phase in turn. You need to take all readings.
I'm not sure if this sounds like I'm taking the mick but it is that simple unless I've misunderstood.

Most 3 phase motors don't have neutrals.
 
Very true!
also on a system with star delta, auto transformer or resistance starting, a reading will have to be taken through this side of the starter.
on VSD's and soft starters, the drive protects the motor from short circuit and overload, and following manufacturers info regarding cable size and length is sufficient.
i still take R1&R2 as I like to ensure all phases are of equal resistance, and it's then on record, but strictly not needed!
 
On the panels that are made in our workshop and sent to site, a 'test' MCB is included using the same size of panel wiring as other circuits to create a negligible impedance. Then once all the appropiate 'dead' tests can be done on the motor circuits, they can be connected to the test MCB and and earth fault loop impedance can be taken without affecting the sensitive gear etc. Obviously take your measured Zs and compare it to the MCB that will be permanently supplying your motor circuit.

You must still measure this Zs/EFLI at the isolator with the isolator OFF. Then measure R1+R2 from the isolator to the motor terminals and add the two together.
 
I presume you are checking for earth loop at the motor connection itself?
Take the connection cover off and clip one lead in to the earth terminal, one to the neutral terminal and then test to each phase in turn. You need to take all readings.
I'm not sure if this sounds like I'm taking the mick but it is that simple unless I've misunderstood.


Hi markythesparky. Thanks for your reply but there is no neutral at this motor...
 
Thanks all for the replies.... Im going to measure the earth fault loop impedance at the isolator for each phase and add R1+R2 to this reading and document all readings on the test cert. From reading the posts this seams to be the way to go....
 
Most 3 phase motors don't have neutrals.

With respect to performing Earth Fault Loop Impedance at the isolator of a 3-phase motor (with no neutral) fed through a VSD I have two queries.


1. Can the test be perfomed with the VSD in the circuit or should it be by passed or perhaps measure EFLI at the incommer of the VSD and calculate R1 + R2 for the remainder of the circuit ?

2. My test kit is a Kewtech KT65 which I believe requires a neutral to perform the test or do I get around this ?

I'm open to ideas. Thanks.
 
Kodr... why are you wanting to test the set-up are you doing a EICR if so the testing is the circuit itself not the equipment/controls attached to it... you shouldn't be performing any tests through the VSD, if you are checking the motor i.e. Insulation resistance then ensure the VSD isn't connected. You need to be very careful you dont damage anything if its a control system including the VSD so isolate the load from the circuit and test the circuit only....BS7671 does not cover the machine/motor control system as such although if it was a simple DOL pump on an isolation switch then usually no harm in testing through.
 
BS7671 does not cover the machine/motor control system

True. I'm not including the motor. Isolator in the off position I just want to know if I can perform a EFLI test whist the VSD is connected or should calculate Zs=Ze + (R1+R2), I appreciate VSD are control equipment but what is normal practice to determine EFLI for these circuits.

Also, in cases where I have DOL motor cicuits with no neutral how is test performed without the neutral, my multifunction test kit (Kewtech KT65) requires a neutral.

Thanks.
 

Reply to testing a 3 phase motor for fault loop impedence in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

G99 SGI-3 4.4 kw set export limit phase to neutral loop impedance test on site 0.309 ohms and dno max being 180 m ohms or 0.018 ohms so site...
Replies
11
Views
1K
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
508
Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
Replies
1
Views
309
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
313

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock