Discuss testing a sub main. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

R

russbrown

Hi could someone help me please. I'm at college doing 2330 level 3. I'm currently doing inspection and testing. I need to know where I find my (r1+r2) on my sub main. Which is powering a double socket and a light. Thanks
 
can't be much of a sub-main then. is it in a shed or garage? to ger R1+R2, you would link L and E at the main DB, then measure at the sub incomer with the sub main switch off. think malcolm beat me to that by a mile, but i've been grafting, not on a cushy posting. LOL. :nopity:soz., malc. couldn't resist. beer's on me when you gey back to civilisation ( ahhh, just remembered, you live in kent. ). :dots:
 
Hi could someone help me please. I'm at college doing 2330 level 3. I'm currently doing inspection and testing. I need to know where I find my (r1+r2) on my sub main. Which is powering a double socket and a light. Thanks

Just for your info mate, as you are in training.

A sub main is exactly the same as any other radial circuit for the purposes of inspection and test, so the test methods are identical.

Where a sub main differs from a radial circuit, is in its application. A circuit which originates at a Consumer unit or similar and goes into the installation to supply lighting, sockets, cookers etc, is known as a radial circuit.

A circuit which originates at a Consumer unit or similar, and then goes to another consumer unit, like house to garage, then this is still wired as a radial circuit, but it is known as a Distribution Circuit (aka sub main).

The two need to be differentiated, because depending on certain things like protective devices, you can have disconnection times that are different on a distribution circuit from a radial circuit.

I will let you find the difference between a ring main, and a ring final circuit for yourself.

Cheers............Howard
 

Reply to testing a sub main. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Is there companies or people out there that can help source sub contract work as im not sure where to start. I know you get recruitment...
Replies
1
Views
418
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
465
hi thank you for help in advance have a potential pv installation for a garage roof that is some 60m from the main house (main incomer in the...
Replies
9
Views
2K
Guidance please - C&G L3 electrical installation - Hotel extension project Hi folks, I am fairly new to this forum but it looks like the...
Replies
6
Views
554
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock