Always do the tests before which are end to ends and Zs at every accessible point on rfc, lighting Zs but at switches if a ceiling full of downlights and dimmers involved, Zs on any radials. L&N - E ir for each circuit. Additionally when more than 1 lighting circuit I do a functional test (look) by disconnecting the neutral to make sure it is not affecting the other circuit (borrowed neutrals). After change Zs on a few random points and compare with original readings to confirm my earth terminations, Ze and rcd trips. Feels like an assessment answer!

Brilliant.
 
Changed 40 in one day, wow. I know I am mainly a fire alarm engineer but even if there is only a lighting, socket circuit in each I cannot see how you can do 40 in a day. Even working a 20 hour day it’s two every hour.
 
Is that a trick question or do you genuinely not know?

Sorry

Yes I know it’s past , as in they have already done 40 consumers units

My point was if they have already done 40 and now looking at possibly doing some testing after the fact , then aren’t they putting cart before the horse
 
Had to change 40 consumer units the other day in a hostel/hotel/b&b and it come to the testing stage


I spoke to the NICEIC who said you need to test circuits for " safety only ". He said doing a global IR test (testing each individual circuit if less than 1M), and earth fault loop, RCD and end to end to any ring mains. He said not to bother with R1+R2 or R2 test as polarity would be verify due to the Zs test.

How much depth do you do?
40 in a day wow, I'd fit one and test it then go for a pint to celebrate a successful day
 
I’ve got it...

They have changed a 40 ‘circuit’ consumers unit the other day

And are now possibly contemplating which tests might need doing and not doing
 
it also comes down to size of the installation, number of circuits etc..
in terms of domestic and not a commercial 3 phase then
As already said by others for me it would be as a minimum
Ring - end to ends
Zs for each circuit as it confirms the polarity, If time permits then R2 with a wander lead or I might link busbar to earth bar in the cu with mcbs all open for a R1/R2 at random points on circuits, if anything pops up then then give that circuit some more attention.
IR - I would as a minimum do LN joined>E if there is lots of neons and fixed lights etc. as It can be a slow process to disconnect it all.
RCD/RCBO trip times on all devices
Then usual Ze, PFC, PSC, check bonding etc..
 

Reply to Testing after a consumer unit change in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
988
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
652

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock