Eric M

-
Reaction score
2
I have a homework question which I hope you will help me with. Heres the scenario.

I am called to inspect a 2 way CCU (in a garage for example) connected via SWA to the main CCU in the house. I notice there are banjo type connectors where the SWA joins the CCUs however there are no earth screws.

I install earth screws and fit fly leads to the earth bars at each CCU.

Question:
what is the correct procedure to test continuity of cpc at the 2 way CCU in the garage? I believe you could use r1+r2 for circuits fed from the secondary CCU but I assume you would also need to check the resistance between MET and secondary CCU earth bar ? Would it be a long lead method from MET to earth bar at secondary ccu? or am I missing something

Hope that makes sense.
 
I'd carry out a Ze (Zdb in this case) test, in the normal way, on the garage CU, which would prove continuity, or not.

The SWA feed to it, I classify as a cct belonging to the main CU, which would be tested when that CU is tested.
 
I'd carry out a Ze (Zdb in this case) test, in the normal way, on the garage CU, which would prove continuity, or not.

The SWA feed to it, I classify as a cct belonging to the main CU, which would be tested when that CU is tested.

I'm with Archy here, and the SWA is a "distribution circuit" not a final circuit, from the main CCU to your garage CCU, so depending on the protective device for that cable, you may have a different disconnection time. If it is protected by a 60898 mcb, then it is still 0.4 disconnection time, but if it is a fuse, it could be 5 seconds.

Cheers.............Howard
 
I'm assuming that they are referring to testing the cpc up to the CU in the garage.
I would isolate garage supply in the main CU, link Line and cpc in the garage, then test R1+R2 for that cable at the main CU. You can add this to your Ze to give your Zdb at the garage CU.
Of course, it could be done the other way round.
 
The more you read the question, the more ambiguous it gets. They don't make it easy sometimes, but it makes you think.
Trouble is they may give marks for one answer and not the other, quite valid, one.
 
I'm with Archy here, and the SWA is a "distribution circuit" not a final circuit... If it is protected by a 60898 mcb, then it is still 0.4 disconnection time, but if it is a fuse, it could be 5 seconds.

Can I ask you where it says this Howard.

I've always been led to believe that final circuits >32A and distribution circuits are 5 seconds (as per 411.3.2) regardless of the protective device.
 
I'm assuming that they are referring to testing the cpc up to the CU in the garage.
I would isolate garage supply in the main CU, link Line and cpc in the garage, then test R1+R2 for that cable at the main CU. You can add this to your Ze to give your Zdb at the garage CU.
Of course, it could be done the other way round.

Thanks for the replies, I think this is the answer I'm looking for. Unless anyone else has any different ideas?
 
Last edited:

Reply to Testing an additional ccu in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
818
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
773
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock