Hi we did a report today and the tails to the mk metal metal consumer unit were through two separate 20mm knockouts. We are now arguing if this should be C2 or C3. Also the main earth entered through the back of the unit. Any thoughts on this ?.
 
The regulations specify that L N and E may only be collectively enclosed by ferromagnetic material when entering an enclosure. And this has been a regulation for longer than MK have been making CU's so nobody can even say it complied with previous regs.
But is it potentially dangerous?
It isn't in normal use as the eddy currents from currents less than 100A are negligable. But under fault conditions there may be significantly more current flowing and much bigger eddy currents.
 
Last edited:
C3 , IMO. i phoned Eddy asnd he wasn't upseyt by excessive currents. in fact, he asked for more in his cookies.
 
The regulations specify that L N and E may only be collectively enclosed by ferromagnetic material when entering an enclosure. And this has been a regulation for longer than MK have been making CU's so nobody can even say it complied with previous regs.
But is it potentially dangerous?
It isn't in normal use as the eddy currents from currents less than 100A are negligable. But under fault conditions there may be significantly more current flowing and much bigger eddy currents.

Hi davesparks,
Thanks for your reply which backed up my thoughts.Although I did opt for improvement recommended to bring the installation to comply with the regulations. The consumer unit has been this way for about 15 years so I could not see how the lead electrician thought this was potentially dangerous
 

Reply to testing code for ferrous consumer unit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
372
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
648
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock