Alright mate,
I take it you’re doing the Napit 7232 to prove competence? If so, read below.
You’ll be given a bay containing a 3P and single phase boards containing various circuits, containment, bonding, sup bonding and wiring types, to simulate something along the lines of a commercial premises downstairs and a residential dwelling above it.
First up you’ll have half an hour to carry out a visual inspection and pick up as many faults as possible, there’s about 12 and they like you to get at least 10. The rest you’ll pick up while testing.
Then you’ll do an EICR on the 3P board in the morning and an EIC on the SP board in the afternoon. You’ll also do a MWC for a spur that’s been put in on the RFC on the SP board.
At this point I’ll note that the 3P board is supplying the SP board.
Go through the testing sequence as you would.
Safe isolation
Continuity of main earthing conductors
Continuity of Bonding and sup bonding
Continuity of circuit protective conductors and RFC’s
IR
Live polarity at incoming tails
Ze
PEFC
PFC
Phase Rotation
Check over the board, make sure you’ve left nothing hanging out, replace guards and board cover.
You can now carry out Zs of circuits, RCD tests and functional tests.
IMPORTANT - Ensure the cover is on your 3P board and your SP board locked off before you take a Zs reading there, as although they’re right next to each other, in reality, ones in a basement and ones up the stairs. You’ll also need to prove safe isolation on the SP board prior to taking the reading.
Time wise, I think you get 2 hours for the EICR and 2.5 hours for the EIC and MWC which is plenty as on a 2391 course you only get 2.5 hours to complete both.
Good luck with but all; and if I’ve put phase rotation in the wrong place, I’m sure someone will be here to correct me shortly.
One more thing - SAFE ISOLATION, SAFE ISOLATION, SAFE ISOLATION