Hi guys starting a new job testing commercial properties, i have passed my 2391 a few years ago and im just looking to refresh myself<

1: when doing an IR test on circuits protected by rcbo's to i have to disconnect both neutral and earth flying leads?
2: what are the flying leads on rcbo's actually for
3: when carrying out a Z's on a socket ring does everything have to be unplugged from sockets
4: same as number 3: for continuity tests


Many Thanks
 
1, Yes disconnect everything, but the cpc's must remain connected to the main earthing terminal whilst the circuit is under test.
2, The cream one is a functional earth, it wont work without it connected, the neutral is to enable connection to the neutral bar.
3, No
4, No, but i would disconnect to ensure no faulty loads give dodgy readings.

I would get GN3 and refresh yourself, it will all come back to you in a flash.

Cheers...........Howard
 
Hi guys starting a new job testing commercial properties, i have passed my 2391 a few years ago and im just looking to refresh myself<

1: when doing an IR test on circuits protected by rcbo's to i have to disconnect both neutral and earth flying leads?

I leave the neutral and earth flying leads in place and disconnect the circuit line and neutral from the RCBO. As above, leave the CPC connected to the earth bar.
 
1, Yes disconnect everything, but the cpc's must remain connected to the main earthing terminal whilst the circuit is under test.
2, The cream one is a functional earth, it wont work without it connected, the neutral is to enable connection to the neutral bar.
3, No
4, No, but i would disconnect to ensure no faulty loads give dodgy readings.

I would get GN3 and refresh yourself, it will all come back to you in a flash.

Cheers...........Howard

On the 'functional earth' point, what do they actually do? they test perfectlt without them
 

Reply to Testing Help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
633
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
622
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
769
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
594
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock