Sorry guys!, im kinda new to this testing stuff.
If you were called to connect a gas solenoid valve to a supply, I take it that it would it be nesessary to check the main gas earthing is in-place beforehand..
If this is so, what test would be required? and how would you do it??
Thanks in advance!
Thanks in advance!
ouch!!!!!
Ok Dan
what you are talking about is the Main Protective Bonding to the gas pipe(because its an extraneous conductive path)
Earthing and bonding are entirely different things, and are there for entirely different reasons
You will be carry out a continuity test using a low resistance ohmmeter, and you will need to disconnect the bonding at one end to eliminate parallel paths
you will quite often need to use a wandering lead to reach from the BS951 clamp back to the MET, remember to null the wandering lead when you null your meter leads;)
I have a feeling we may be chatting quite a bit in the near future.....:p
Thanks Shakey!..
Yeah i must agree with you there.. You seem to know you stuff and hopefully i can get more advice from you..
Thanks Again
Thanks Shakey!..
Thanks Again
no problems, there is a good range of knowledge on this forum, i teach this stuff so i am 'up' on the regs, testing etc
Others have deep knowledge in different areas
ask away old chum;)
Reply to Testing Main Gas Pipe in Commercial Kitchen in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi Everyone, Sorry in advance if this is a silly question. There is a junction box in my mother's kitchen, on the wall above her kitchen...
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...