Practicing again...
TN-CS Supply New Built Home
Tested ring final circuit..
P - 0.34
N - 0.34
CPC - 0.59
________________________________________________
N1 - P2 = 0.70
N1 - P2
P1 - N2 = 0.16
P - N Sockets..
1- 0.19
2- 0.16
3- 0.17
4- 0.17
5- 0.18
6- 0.16
7- 0.21
8-
9- 0.18
________________________________________________
P1 - CPC2 = 0.95
CPC1 - P2
P1 - CPC2 = 0.21
P-CPC...
1- 0.23
2- 0.22
3- 0.26
4- 0.22
5- 0.23
6- 0.30 ? Why the high readings on socket 6/7/9..?? really annoys me.. No test i do ever goes right.
7- 0.36 ?
8-
9- 0.30
________________________________________________
Socket "8" was not accessible.. What do you do about this.. What would you write about this on Cert?
________________________________________________
Ze = 0.21
PFC = 1.23 kA
________________________________________________
IR Test..
L-N >1000
L-E >1000
N -E >1000
________________________________________________
Does all look ok ???
TN-CS Supply New Built Home
Tested ring final circuit..
P - 0.34
N - 0.34
CPC - 0.59
________________________________________________
N1 - P2 = 0.70
N1 - P2
P1 - N2 = 0.16
P - N Sockets..
1- 0.19
2- 0.16
3- 0.17
4- 0.17
5- 0.18
6- 0.16
7- 0.21
8-
9- 0.18
________________________________________________
P1 - CPC2 = 0.95
CPC1 - P2
P1 - CPC2 = 0.21
P-CPC...
1- 0.23
2- 0.22
3- 0.26
4- 0.22
5- 0.23
6- 0.30 ? Why the high readings on socket 6/7/9..?? really annoys me.. No test i do ever goes right.
7- 0.36 ?
8-
9- 0.30
________________________________________________
Socket "8" was not accessible.. What do you do about this.. What would you write about this on Cert?
________________________________________________
Ze = 0.21
PFC = 1.23 kA
________________________________________________
IR Test..
L-N >1000
L-E >1000
N -E >1000
________________________________________________
Does all look ok ???