TNCS - 0.35
TNS - 0.8
TT - 1667 although 200 is acceptable but it could be unstable and so should ideally be under 100.

Page 11 OSG


Cheers J

I've measured Ze on a TT as 0.27

Would you say ive messed up somewhere on the test as this seems VERY low ???
 
Cheers J

I've measured Ze on a TT as 0.27

Would you say ive messed up somewhere on the test as this seems VERY low ???

If you positively isolated the Main Earthing conductor from the Earth bar and main bonds then you will probably be reading through a parrallel path close to your earth rod...maybe a water or gas pipe....if this is your reading then record it on your test sheet but note down your reason.
 

Reply to Testing.. Never goes right.. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock