Bear with me, I haven't seen the setup in question so I can only go on what I've been told........
We had a swimming pool pump that locked up after the bearing failed and then tripped the 63A/30mA rcd, presumably after the insulation had broken down. The pump runs through a contactor operated by a time clock, the clock had been set to permanently on for a few years so that wasn't an issue. The contactor has an overload attached which was set at 6.5 which seems right for a motor rated at 6/9A run/start up. The replacement motor has been fitted and is running fine but it is rated at 7.2/10.1 run/start up and is through the same overload set at 5.5A (to test it).
Is there a way of testing an overload or does this seem normal? How can we prevent this motor doing the same?
In case you're wondering I am a sparky and have the usual multimeter and mft.
We had a swimming pool pump that locked up after the bearing failed and then tripped the 63A/30mA rcd, presumably after the insulation had broken down. The pump runs through a contactor operated by a time clock, the clock had been set to permanently on for a few years so that wasn't an issue. The contactor has an overload attached which was set at 6.5 which seems right for a motor rated at 6/9A run/start up. The replacement motor has been fitted and is running fine but it is rated at 7.2/10.1 run/start up and is through the same overload set at 5.5A (to test it).
Is there a way of testing an overload or does this seem normal? How can we prevent this motor doing the same?
In case you're wondering I am a sparky and have the usual multimeter and mft.