J

james86

I have been asked to test an offpeak cdu but what am I to do with the live tests? Do I calculate using them using ze from on peak cdu? Or do I go back at night!? Lol. Also what about schedule of inspection for functional tests??? Cheers
 
you hang around till the power comes on at 12am!!!

alternatively you LIM the live tests and calculate ZS from R1R2 + ZE (main incomer on live side)

you also LIM the functionaal tests or you disconnect and put you continuity meter either side of the switch!!
 
Yes, you do as Durham suggests or you energise (safely) the off-peak board from the 24-hour supply for the purpose of live testing.

If this is a periodic inspection then I'd go with Durham, initial verification and I just have to see everything working!
 
Firstly. Yes it is pir, confusion set in because client had spark who refused to test that board because of the off peak nature!

Secondly. Thanks for that, never thought of doing functional test like that on a storage. Won't the element just give continuity thow ????
 
Firstly. Yes it is pir, confusion set in because client had spark who refused to test that board because of the off peak nature!

Secondly. Thanks for that, never thought of doing functional test like that on a storage. Won't the element just give continuity thow ????

You will get a resistance reading through the element(s) but you'll also be able to check the switching of the input thermostat controls.(assuming storage heating)
 
Last edited:
Cheers guys, I think in order to energise it would involve breaking seal on storm fuse because there is no isolator!? I know what u mean though about seeing everything working. I got to say this forum is the best thing since sliced bread, I am getting loads of answers! Once again many thanks chaps
 
Cheers guys, I think in order to energise it would involve breaking seal on storm fuse because there is no isolator!? I know what u mean though about seeing everything working. I got to say this forum is the best thing since sliced bread, I am getting loads of answers! Once again many thanks chaps

It is a great forum, don't forget the 'thanks button' ;)
 

Reply to testing off peak consumer unit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
692
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
374
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock