Discuss testing procedure for garage consumer unit in the UK Electrical Forum area at ElectriciansForums.net
PJW
I'm in the process of fitting a CU in my workshop can anyone tell me do i do testing at the new 2 way CU as i would on a domestic one or the main one in the house or both? I was thinking both
Before anyone says get a electrician in to do the job i'm a NICEIC domestic installer just not done this kind of job before.
Test the supply cable to the new workshop CU. test for R2, IR, etc.. is the cable suitably rated for the load. is it correct cable and installed correctly.. Also check the earthing... does the workshop have extraneous metal parts? if so and you have PME have you put a rod in or run a suitably sized earth cable to the workshop?
Then test the CU in the workshop as you would any other, i always treat the supply from main cutout/CU as circuit 1. others might just cover the new circuits in the workshop CU.
You may be a NICEIC DI but its a tad disconcerting that you have asked this?
this is the sort of reply i was expecting, shame
You need thicker skin matey.
You will be responsible for the circuit to the garage, the garage cu and all the garage circuits. Plus of course the earthing and bonding in the house.
It is a bit worrying that this is unclear in your mind.
Don't forget to give the client the certificates and the part P notification.
PJW how come you became a DI with nil qualifications or is the omission on your profile wrong.
NICEIC domestic installer but doesn't know when to test a board? Isn't that a necessary skill to become an NICEIC DI?
It's a new board and requires Initial verification, schedule of test results and schedule of inspection. But you know that, Don't you?
Apparently not in this case
Gasp, you have won PJW, You are my first "GASP" Post since being allowed back on parole
Reply to testing procedure for garage consumer unit in the UK Electrical Forum area at ElectriciansForums.net
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
4K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...