Guess, strictly speaking it depends on what material it is terminated into.
 

ipf

-
Mentor
Arms
Esteemed
'MICC' for me. Whatever the actual csa, I'm sure it is going to easily meet requirements.
 

davesparks

-
Mentor
Arms
Esteemed
Yes, the sheath CSA is bigger than that of the line conductor for all multicore MICC as far as I know so will be the correct size. It's only the method of connecting to the sheath that may restrict the size.

It think the larger single core cables have a sheath CSA smaller than the conductor.
 