iceman

hello im tryin to get ready for me assesment with the nic iv got a ring final circuit upstairs witch provides power to the central heating off a fuse spur when testin R1 + R2 do i test all sockets and the spur or just the sockets? thanks

also theres a garage supply comin frm a 20A circuit breaker frm the house providing power via a fuse spur 2 socket outlets and 3 light points when testing R1 + R2 do i test every point including the spur? thanks
 
yes the sockets are on a radial circuit when i practicing i went straight to the furthest point but on the day the asseser will probley want to see me test every point :-/ lol
 
Just out of interest, why would he want to see the test at every point?

Edit. Duuuhhh. Just realised what i said.:D:D

Sorry, i've been out in the fresh air all day.
 
Last edited by a moderator:
why would you take a R1 + R2 on a radia (R1 + R2 only on a ring)l and how can you take a R1 + R2 reading on you central heating surly it would just be a R2?
 
One point to bear in mind is that if measuring on the load side of a fcu the acceptable value will depend on the rating of its associated fuse and not the circuit protective device at the consumer unit.


spark1
 
Because you are measuring the possible fault path of that circuit to see if it is within the limits required

sorry i thought you only nedd to take a R1 + R2 reading on a ring, just new to testing tho.
 

Reply to TESTING R1 + R2 garage supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock