Discuss testing R1 + R2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

VoltzElectrical

-
Esteemed
Reaction score
2,100
When testing R1 + R2 on a three phase circuit, do you connect each phase in turn to earth and test at other end? Record the highest value? Similar to what you test Zs on 3 phase but without the connecting?

Cheers all.
 
Hi Voltz remember you are checking continuity of the CPC the R1+R2 method is just a convenient way of doing this.
If it is a 3 phase circuit it is good practice to check all three but if wired and connected correctly the readings should be the same Each phase conductor is the same CSA and the same length. if you get different readings there is a problem somewhere.
 
platty,
You are perfectly correct Sir, however, the idea of checking the 3 is to ensure that there are no issues with connections, and this is a good way of ensuring that the line resistances are acceptably balanced as well as checking R2 at the same time.
This is why I always recommend checking all 3, also you should record the highest resistance on your results sheet.
 

Reply to testing R1 + R2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
392
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
811
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you...
Replies
0
Views
431
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you should...
Replies
0
Views
483

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock