i guess it's each to their own, but i don't think i'd be running SWA without a dedicated CPC, just what i was taught i guess
 
The electricity board relay totally on the armour in a TN-S system and TN-C-S sysyem. Regs say its fine so really cant see the problem with using the armour as the sole means of earthing.
 
ive seen allot of sparkys write (sheath) where you would normally write the size.makes sense to me as the armouring is a sheath.
 
HI,
The nic have a guide for this within one of their books.I had the same problem recently on a periodic test.The flats were built early 1980s and 2 core swa was used.It turns out that 16mm 2 core swa is equal to a 10 mm earth on the armour.I agree we would not rely on this now but my loop readings were fine so could not fault it.I also contacted the manufactors of the swa who confirmed the same.
 
NO NO NO - i believe you are very wrong there!

the armouring is not designed to be relied on as an earth connection!

the armourings reason for being there is to offer mechanical protection, end of - the earth connection is a benefit. the armourings are there to try and protect the cable from being cut through, which is why you use ARMOURED cable! armour is armour, earth is earth

i'm not saying it can't be used, it is (i believe) good practice to ensure if there is no core to be used as an earth then a seperate earth will be run. the csa of the armourings meets the requirements of the regulations (unless you start using single cores or two core SWA with conductor CSA's of greater than 120mm)

whilst it may be adequate on installation, with 5 years of degredation (depending on the environment) it could easily break down/rust at the glands or any breaks or water ingress into the pvc sheath.

if it's possible i'd always run a seperate earth, and it is in most circumstances i think reasonable to do so

I'm a bit confused
Two different views in two posts, So do you always run a separate CPC or do you sometimes rely on the armour even though you appear so against it
 
The selection and erection guidance note (don't have it here so can't remember specifics) tabulates most pvc and xlpe armour sizes and also states if the armour is adequate for use as the cpc without a parallel cable.;)
As far as I'm concerned if the CPC is run as a core within the cable I'll bond one end of the cable with a bolt and banjo, if the armour is to be used I'll banjo it and flylead it BOTH ENDS with a cable of a suitable size for a cpc so for the sake of argument 6mm/2.5 is standard T&E then a 2.5 single will be adequate as a flylead for a 6mm SWA.
 
Back to the original question....

There are tables in guidance note 1 which will tell you which cables can be used, pages 171 to 173, tables D9, D10A and D10B.

Therefore, would these tables be put in a guidance note if this was not an acceptable practice?
 

Reply to Testing SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock