Quite a simple Q really - how would you go about testing an installation where you change the main CU but don't change the 'sub main' powering an extension. Also, I am changing the board to a 17th ed board - does the sub main 'automatically' need upgrading? At the moment it is fed via a 45A MCB (16mm t&e).
 
Quite a simple Q really - how would you go about testing an installation where you change the main CU but don't change the 'sub main' powering an extension. Also, I am changing the board to a 17th ed board - does the sub main 'automatically' need upgrading? At the moment it is fed via a 45A MCB (16mm t&e).

Cirrus, you just test it as you would normally.

On the cet you put 'extent of installation covered by this certificate', and as long as that reflects what you have actually tested, then thats fine
 
'extent of installation covered by this certificate' - what does that actually mean though Shakey? Am I saying that I have tested everything in the house by puting that on?:confused: And are we saying I have to test the 2 boards or just the one I am changing?
 
Last edited by a moderator:

Reply to Testing two CU's in one house in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
257
Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
414

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock