stop me if i am wrong but the certs ask for the MAX efli for that circuit, so if we have a pendant (end of line) at the top of stairs, and is 2 way switched, then obviously the max reading would be at the remote switch.
 
stop me if i am wrong but the certs ask for the MAX efli for that circuit, so if we have a pendant (end of line) at the top of stairs, and is 2 way switched, then obviously the max reading would be at the remote switch.

if its done 3 plating at the pendant, then thats where the max Zs would be;)
 
I would love to know what the megger rep says as some of the sparks I work with have been told that that particular test instrument does give you an r1+r2 reading. I have never used this reading myself as you are never asked to submit a ze reading that the machine can deduct the zs from ze to give you r1+r2 so as far as I can see it would be impossable for a tester to give a reading even if it was just deducting ze from zs. I probably have'nt explained it very well but according to the rep just by doing a test for zs the tester will give an r1+r2 just by doing this one test and nothing else.
 

Reply to Testing Zs at Lighting switch's with no neutral in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
581
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi, I need some advice on the wiring for a new ceiling light. I have taken down the original light, and I'm left with the wiring in the image...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock