:confused:Is there any ruling/guidelines that state that you cannot test for efli of the lighting circuit at the light switch providing your meter does not need a neutral to power it up? as it is easier and often less hassle with light fittings in many houses today?
 
:confused:Is there any ruling/guidelines that state that you cannot test for efli of the lighting circuit at the light switch providing your meter does not need a neutral to power it up? as it is easier and often less hassle with light fittings in many houses today?

well what you have to consider Tony, if you are using presumably a three plate ceiling rose, then the light swtich is not the extremity of your circuit

As you know, the value of R1+R2 and Zs entered on your test results are the HIGHEST reading for each final circuit

If you are three plating then this will be at your rose, not the switch

Consider a 2 way lighting circuit, depending on the configuration, you could be adding 10m-20m easily by the time it goes up and down your strappers

and anyway under the 17th, when more light circuits come under RCD's, if you are measuring on 'no trip loop' or equivalanet, a lot of meters will need that neutral!;)
 
well what you have to consider Tony, if you are using presumably a three plate ceiling rose, then the light swtich is not the extremity of your circuit

As you know, the value of R1+R2 and Zs entered on your test results are the HIGHEST reading for each final circuit

If you are three plating then this will be at your rose, not the switch

Consider a 2 way lighting circuit, depending on the configuration, you could be adding 10m-20m easily by the time it goes up and down your strappers

and anyway under the 17th, when more light circuits come under RCD's, if you are measuring on 'no trip loop' or equivalanet, a lot of meters will need that neutral!;)

cheers pal fair comments
 

Reply to testing Zs at the light switch in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
550
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
Replies
10
Views
852
Hi all, after a bit of advise if ok please. We have a switch which currently only powers one single LED down light in our ceiling. From this...
Replies
6
Views
1K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock