Discuss Testing in the Electrical Forum area at ElectriciansForums.net
Are you saying u don’t have to remove bulbs when testing for earth continuity.you don't remove for a continuity test. but without removing all loads, you can't do a L-N IR test.
no you don't need to remove. you are measuring either R2 or R1+R2. as the bulbs are connected L-N, their resistance will have no effect on your readings.
its just that in college, they said lamps should be remved for R1 R2 testno you don't need to remove. you are measuring either R2 or R1+R2. as the bulbs are connected L-N, their resistance will have no effect on your readings.
ask them why.its just that in college, they said lamps should be remved for R1 R2 test
Yeah you’re right, the tests done in college are for a new installation, looks like with a existing lighting circuit, the lamps don’t need removing .Perhaps they are teaching you how to conduct the series of tests for an installation, not just continuity. In that case, all loads would need to be removed first.
Actually, during initial verification cpc continuity must be verified at all points.During initial verification, r1+r2 or r2 needs to be confirmed at the furthest point. The only way to measure r1+r2 or r2 is physically removing the lamp/cover and gain access to the conductors.
If you are performing r1+r2 this is a good time to confirm polarity too using the light switch.
Just to correct you...…..AND goodwill....etcI do like the way some people like to correct other people in terms. Peace on Earth on Goodwill to all Men etc.
Up yours, just edited itJust to correct you...…..AND goodwill....etc
on lR test do the rcds switched to off .Actually, during initial verification cpc continuity must be verified at all points.
Have you got an RCD warning label to read?on lR test do the rcds switched to off .
I was asking if the RCDs are switched to the off position during insulation resistance test, as I know they are sensitive equipment.Have you got an RCD warning label to read?
If not, look it up in the regs. or on line, even.
On IR test can u just switch RCDs off or do u actually have to dis them.you don't remove for a continuity test. but without removing all loads, you can't do a L-N IR test.
Disconnect them it was meant to sayI was asking if the RCDs are switched to the off position during insulation resistance test, as I know they are sensitive equipment.
[automerge]1577561827[/automerge]
Sorry disconnect them , my post was meant to say.I was asking if the RCDs are switched to the off position during insulation resistance test, as I know they are sensitive equipment.
I believe you are correct. I thought it was Zs that had to be proved at every point but yes, I believe it is continuity of cpc at every point.
A Zs wouldn't confirm a cpc is present or that it is a acceptable condition or terminated sufficiently
You can't carry out Zs until the installation is energised, and you can't safely energise an installation without proving the correct connection of the protective conductor at every point.
This is why the continuity of the protective conductor is tested first.
Reply to Testing in the Electrical Forum area at ElectriciansForums.net