Hi all just installing a 3 p extractor fan and in the instructions which are in broken english it says it needs thermistor protection would this just be wired back to the dol starter and wired in line with the contactor circiut ai through the thermsitor relay( which i presume is normanly closed) them to the motor and back to a2 cotactor terminal
cheers
 
OP
K

Knobhead

The two leads from the thermistor wire direct to the relay. The relay will have both NO/NC contacts that you can wire in to the DOL starter to suit you.
 

SteveG

EF Member
Messages
23
Location
West Yorkshire
Actually, it depends on the thermistor. Some go open circuit when a certain temperature is reached and some are resistive that change resistance with temperature and need a special thermistor relay that has to be reset.

To be honest, I rarely see them connected at all (especially in fans as by their very nature they blow cool air over themselves) As long as the overload is set exactly right - they'll trip if a problem occurs.
 

Pete999

Mentor
Electrician's Arms
Messages
22,966
Location
Northampton
The fan won't be blowing cool air over the motor, the fan is being used in an extraction situation the air will more than likely be very warm and humid
 

DPG

Respected Member
Electrician's Arms
Messages
5,469
Location
S Yorkshire
I think he's sorted it now. He's had 4 years :) Daz
 

SteveG

EF Member
Messages
23
Location
West Yorkshire
hahaha. The thread showed up below in the similar thread thingy.... I didn't check dates. :)

Ah well, it might help anyone reading later.
 
  • Like
Reactions: DPG

DPG

Respected Member
Electrician's Arms
Messages
5,469
Location
S Yorkshire
Yeah the similar thread thing has caught me out before!
 
OP
S

spary

I'll just add that thermistors must be used on motors running in hazardous areas that are using speed control
 
OP
K

Knobhead

Actually, it depends on the thermistor. Some go open circuit when a certain temperature is reached and some are resistive that change resistance with temperature and need a special thermistor relay that has to be reset.

To be honest, I rarely see them connected at all (especially in fans as by their very nature they blow cool air over themselves) As long as the overload is set exactly right - they'll trip if a problem occurs.

You are talking of thermal fuses not thermistors. They are only used in small cheap motors.