Haha. Well this is awkward…

I’ve just reported #29 as a possible bot / hacked account as I couldn’t see how the content referred to the thread…. But as there has been messages since by the same author, I may have jumped the gun somewhat.

Apologies.
 

Rockingit

-
Mentor
Esteemed
Arms
Supporter
Reaction score
5,215
It's cases like this where it's the duty of the Inspector to remember the first principles of the task - is it fit for continuing safe use?

Yes, we use markers and references to various regulations to help us make that decision and that now outdated concept of 'did it meet the regs in place at the time' is thankfully no longer an opt-out, but ultimately it's the experience and judgment of the inspector that's on the line. For example - you IR a circuit buried in an old hollow wall and get a reading of 2.1MOhm, technically that's compliant so not notable, yet to any of us with experience it instantly rings alarm bells and is probably either very old cable at the point of severe deterioration or vermin damage. So now you have to consider continued safe use, not just what's on your meter. And that decision probably isn't just electrical, it's informed by all the other adjacent information around us - is that cable buried in a stone wall or does it likely run up through that roof void full of tinder dry old crispy mice nests...... etc.

It's a responsible thing to do, which is why all these fly by inspection companies boil my pee so much.
 
OP
littlespark

littlespark

-
Esteemed
Arms
Reaction score
14,784
not come across any spurious readings so far, but I bet the 80/90’s t&e will break down before any bulletproof MICC….
A bad pot would have failed well before now.

The cost of replacing fuse boards when some are built into bigger panels is going to be cost prohibitive, but there are some rcd sockets been fitted in rooms that were used for catering.

Other boards have been changed in the past where the old fuse board has been used as a joint box and a newer CU fitted.

Can’t wait to open than literal can of worms.
 

pc1966

Esteemed
Arms
Reaction score
9,901
Unless you had a duff brand/batch of T&E its usual downfall are mice, UV exposure, or mechanical abuse (trapped, nail, etc).

I too would be very weary of IR readings below 10M unless I could identify why!
 
OP
littlespark

littlespark

-
Esteemed
Arms
Reaction score
14,784
Unless you had a duff brand/batch of T&E its usual downfall are mice, UV exposure, or mechanical abuse (trapped, nail, etc).

I too would be very weary of IR readings below 10M unless I could identify why!
There could be mice… possibly.

It’s a shame when an otherwise great installation with neatly clipped MICC, surface conduit etc gets ruined by a bit of sticky backed mini trunking down the side of a lovely period architrave.
 
OP
littlespark

littlespark

-
Esteemed
Arms
Reaction score
14,784
Getting well into the workshop today… just the general power and I’ve got issues.

So it’s the white CU I’m testing in the middle.
Top left MEM SW/fuse feeds the cafe, top right feeds the public toilets and in turn, the two holiday cottages.
Bottom left is main sw/fuse “M” turns off everything. And bottom right is busbar chamber that everything feeds off.

Haven’t checked fuse sizes in “M” yet. Cannot isolate white CU without turning off cafe and cottages. Whatever size is in “M” is the OCPD for this white CU. I’ll find out when I can turn off the cottages… there’s guests in just now.

But… from the CU. There’s an rfc with 3 doubles. From this, an unfused spur goes into the shop next door… for another 8 points!
I’ll either suggest fusing down here, or pulling out the spur, extending the cable back to CU and making the shop its own radial circuit.

Workshop and shop also share the lighting circuit. Could do with separating that as well.

Only 4 circuits out of a 5+5 dual rcd board used, so plenty spares.

The 2 RCDs are tripping out at 46 and 62 ms. At x1 I



This is going to take me weeks..... 65CCBA28-ECB6-4461-93F1-55FC544C589E - EletriciansForums.net
 

Reply to This is going to take me weeks..... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi I posted a few weeks back what looks like to be an economy seven timer located in a store cupboard in my flat that I assume was connected to a...
Replies
3
Views
921
customer rings up ,I had a electrician round to put some sockets fronts in the front room and he told me you can use the sockets bar the socket...
Replies
18
Views
3K
Hi all, need some opinions on the following please> Origin is a three phase 60A TN-C-S supply.it goes into a changeover switch (small PTO driven...
Replies
59
Views
4K
W
Hi. This is my first post so if any admin see this, I'm sorry if I'm breaking any rules! Anyway let's get down to it. I've recently found myself...
Replies
36
Views
2K
wistedranks
W
B
Just back from sorting a call out, just can't believe I'm Sparky no 3 !!! Background story. Office reception area with newly fitted wrought iron...
Replies
24
Views
2K

New Posts (Please Reply)

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top