Hi all I am currently on a site and just pulling some data in the plant room and noticed this :-

Main LV panel
3 phase breaker rated 125amp with 25mm non armoured tails and 16mm earth supplying landlord board run in trunking with 27 other swa 16mm 3core

Then off the 3phase bus bars we have 3x 250amp 3phase breakers with 25mm non armoured tails running off to 3 seperate 3phase boards supplying 11apartments from each board split over 3phases again with a 16mm earth and run in with 27 other 16mm swa 3 core supplying the sub boards protected by a 63 amp breaker.

My understanding is that a 25mm single core non armoured cable 3phase run in trunking can only hold top end of 80amp (not sure of exact top of my head)

And same again with 35mm can only take 110ish in same situation...

Any thoughts?
 
the rating of the breakers is irrelevant as long as they,re rated high enough for the load. the only thing of concern is the OCPD ratings being correct for the cables which they protect. (In<Iz).
 
Cheers telectrix,

So your talking our 250amp overcurrent protection not being suffiectient to protect 25mm single core then?
 
oops, misread part of the OP. didn't see that you'd put 250A breakers. the 25mm tails should be protected by no more than 100A breakers. are they deffo breakers and not isolators?
 
Seems a little strange that these MCCBs are so overrated for the cables they are protecting. The only other thing i can think of (if these breakers are not oversized) is that many get confused by the printed label frame size, for the actual rating size. As it's often the case, that the rating size is indicated in much smaller print

Anyway if what you are saying is correct, then i can't see why you wouldn't bring your observations to the notice of the responsible person for this installation....
 
It goes 400amp main isolator, then bus bar, then tapped off bus bar what looks to be manufacture tails 35mm from each phase supplying 3 3phase 250amp mccb's then 25mm no armoureds through trunking to 3 seperate 3phase dis boards.
 

Reply to Thoughts on plant room do I speak up? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
854
Hello all. 17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident). Just bought a house with a 16mm 3...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock