hello everyone, I have a little problem. I've got a three phase board, it has the three phase sauna, one phase lighting and sockets connected to it. The problem i am facing right now. This is a comercial unit. So the problem is that the sauna makes the RCD trip every so often. And the board is protected by only1 RCD as a main switch. So when RCD trips the whole lighting and other circuits will be disconnected. This is causing a lot of hassle for the customer. And he's wondering if there is anything to do, add additional RCD or do something else without spending a fortune on this.
I have attached a photo so you could better understand what I mean
 
Last edited by a moderator:
And he's wondering if there is anything to do, add additional RCD or do something else without spending a fortune on this

That depends on what the customer considers to be a fortune, some people would consider a £100 solution to be a fortune whilst others would be happy to pay £1k/£1.5k to replace the DB with one which would better suit the requirements.

What does, or does not, actually require RCD protection in this installation?
How many circuits are there in total?
 
I would start by looking into WHY the rcd is tripping.

it would be better to find a potential fault that is developing than find a way to avoid it tripping.
 
I would start by looking into WHY the rcd is tripping.

it would be better to find a potential fault that is developing than find a way to avoid it tripping.
RCD is tripping when people pour too much water on the sauna stones. And that's for protection obviously. So I qas thinking if I could separate sauna circuit and the rest of premises, so if the sauja trips, it wouldn't take the power out in the whole board.
 
What make and type is the board as you may be able to replace the main switch, fit rcbos for the single phase circuits and a separate rcd for the sauna but as @James says solving the tripping issue is what you should be looking at.
 
RCD is tripping when people pour too much water on the sauna stones. And that's for protection obviously. So I qas thinking if I could separate sauna circuit and the rest of premises, so if the sauja trips, it wouldn't take the power out in the whole board.

Then there is clearly a potentially dangerous fault with the sauna which needs fixing.
 
Is the main board RCD at 30mA type? They are prone to tripping on cookers, etc, with a small amount of damp absorbed by the element so it would not be very surprising if they go on a sauna!
 
Then there is clearly a potentially dangerous fault with the sauna which needs fixing.
Thank you
Is the main board RCD at 30mA type? They are prone to tripping on cookers, etc, with a small amount of damp absorbed by the element so it would not be very surprising if they go on a sauna!
On the RCD it says 100A 3P
 

Attachments

  • Screenshot_20200512-153848_Gallery.jpg
    114.3 KB · Views: 16
It's 30mA, if you zoom in a bit you can see it.
OK, that sort of confirms it.

The best suggestion is from @westward10 and as it looks like a Hager board you can probably get RCBO for the single phase circuits easily enough. However, I'm not sure you will find a RCBO to replace the 3-pole MCB in that board (and no space for another pole beside it) so your best/cheapest option might be:

  1. Replace the RCD incomer with a switch (4P matches, but 3P might be fine).
  2. Replace the single pole MCBs with RCBOs for all circuits needing that protection (sockets, lights, etc)
  3. Put the RCD incomer from (1) in to a "garage CU" enclosure to provide separate protection for the 3-phase supply to the sauna.
Maybe others will have better ideas?

It might be worth inquiring of the sauna company what sort of RCD protection the recommend, as 30mA might be less than normal for that sot of load (assuming cable route does not require it).
 
Last edited:
OK, that sort of confirms it.

The best suggestion is from @westward10 and as it looks like a Hager board you can probably get RCBO for the single phase circuits easily enough. However, I'm not sure you will find a RCBO to replace the 3-pole MCB in that board (and no space for another pole beside it) so your best/cheapest option might be:

  1. Replace the RCD incomer with a switch (4P matches, but 3P might be fine).
  2. Replace the single pole MCBs with RCBOs for all circuits needing that protection (sockets, lights, etc)
  3. Put the RCD incomer from (1) in to a "garage CU" enclosure to provide separate protection for the 3-phase supply to the sauna.
Maybe others will have better ideas?

It might be worth inquiring of the sauna company what sort of RCD protection the recommend, as 30mA might be less than normal for that sot of load (assuming cable route does not require it).
Thank you very much for your answers. That helps a lot to understand which is the best option. And if anyone else has any other options i would like to hear them please.
 
This is what you need to replace the rcd switch.
So I have to replace all mcb's to rcbo's and replace rcd to this switch? What about the 3P mcb?
 
Yeah, my idea would be to find the fault that causes it to trip when water is poured on the stones in the sauna. This sounds like a definite link has been made between this action and the tripping of the RCD, so it needs to be investigated.
Yes, a couple of things to find out, such as did it always do this? (i.e. is a 30mA trip too low for that sort of installation) or has something changed.

It might not be the actual sauna heater of course, it could be that a light in the sauna is letting steam in and causing the earth leak. Maybe someone put in a replacement without suitable IP ration, or maybe it has special seals around them that have degraded with time, etc.?

That is the problem with a single RCB and intermittent trip - they might find it is actually a light circuit or similar that is causing it to trip.

Maybe @Vinnie2020 can get them to run it and make it trip then quicky isolate all the MCBs and see if an insulation tests reveals a leaky circuit before it dries out.
 

Reply to three phase board separation in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
516
I’m currently doing some testing on some site temps I have a three phase trip system the tails from the head go into a 100 amp RCD which feeds a...
Replies
8
Views
1K
Hi everyone, each leakage question here. I am needing to run some LED screens, professional type, not TVs. These are 500mm x 500mm panels and...
Replies
11
Views
3K
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
815

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock