Hello all, I recently was asked to quote a three phase motor install within a pallet factory. To be honest, I was somewhat stumped in how to attack it as the sheer size and the control cabinet was gigantic. Although I'm mainly a domestic, commercial spark, this was somewhat out of my league. The motor was rated at 90kw, three phase, pf was 0.85, so current would of been around 150 amp per phase. The supply coming in was a 200amp, possibly 250 ( I don't remember exactly) and a standard three phase consumer unit. The control unit had an array of contactors and overloads, now I'm ok with motors and starters to a certain degree, ie forward reverse, on delay off delay, start delta, but this was out of my league. My questions are as follows as..
Would this require a separate circuit with a large type three phase isolator just for the motor? IE fed from a bussbar chamber.
Who would I need to speak to, IE in this regard as most sparks would struggle including myself, thank you in advance
 
Usually the machine manufacturer has done most of the work for you, on the machine nameplate or instructions will be the machine power requirements.

I.E. 400v 3ph 200A

solve it the same way you would approach any new circuit, calculate your cable size and ensure the isolator is able to accept both the current and the size of cable required.

as for a suitable breaker, some distribution boards allow for breakers in the 200A range, check with the manufacturor of the board.

if not, often a fused isolator is the easiest way to go and yes if there is a bus bar chamber feeding the boards then that may well be a suitable place to take the supply from.
 

Reply to Three phase motor help in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Hi, I am trying to wire a two speed switch to a three phase motor. I have continuity checked the switch in both positions 1 - Low and 2 -High (See...
Replies
1
Views
2K
Hi guys, Is there a standard tolerance percentage that should be followed when checking the winding resistance of each coil on a three phase...
Replies
3
Views
6K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
This might sound like a stupid question so apologies in advance. So I had a random thought in my head. So I was wondering if I was to use a...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock