Discuss Three Phase overhead supply is it TN C in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
While carrying out a EICR I found on first inspection that there were no RCDs installed . When I checked at the Pole Mounted Transformer the Earth & Neutral were connected at the Neutral point. So am I right in concluding it's a TN-C System? The 17th Edition states that RCDs should not be installed where a TN C System is used (411.4.4)
I will take a pic tomorrow,but it looks like the Earth and Neutral are connected at the transfer. The reason I am suspecting is a TN-C is the lack of RCD protection on the Ring main final circuits. If it was a TT it would be protected with RCD at the mains
Yes, or any final circuit in the building, by the way it feeds a hotel. The overhead feed is by way of bundle conductors (4) sorry that's a South African term. I don't know what you call them here?
Eh?
The 17th Edition states that RCDs should not be installed where a TN C System is used 411.4.4
The following types of protective device may be used for fault protection:
(i) An overcurrent protective device
(ii) An RCD.
It'll be a PME supply. Concentric cable split at the installation intake, to N & E.
Eh?
(ii) An RCD.
Read on a couple of lines after Note 1
"An RCD Shat be used in a TN-C system"
My house has a two wire supply coming in along the outside wall, it was clearly a TT in the past but has been converted to TNC even though the supply is via 2 individual separate single cores.
The DNO risk access any existing TT before conversion I am led to believe, I see no reason why your install won't have been converted at some point even an overhead supply.
You probably have TN-C external to the building then the PEN conductor is separated at the service head which gives the S on TN-C-S.
Reply to Three Phase overhead supply is it TN C in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...