Discuss Three Phase overhead supply is it TN C in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
While carrying out a EICR I found on first inspection that there were no RCDs installed . When I checked at the Pole Mounted Transformer the Earth & Neutral were connected at the Neutral point. So am I right in concluding it's a TN-C System? The 17th Edition states that RCDs should not be installed where a TN C System is used (411.4.4)
Far more likely to be a PNB supply which is a form of TNCS.
A lack of RCDs does not dictate what the supply type is, its either a sign of the age of the installation or of non compliant work.
Reply to Three Phase overhead supply is it TN C in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...