Hi everyone.

please comment on the earthing of three phase as a new installation .
Then are you allowed to use the armour or not and what is the Regulations about earthing when there is a cable with 4 core but you need a neutral and a earth plus the 3phase..?

Many thanks

M0LVW:dizzy2:
 
Your profile gives you as both domestic and Industrial, this is not a question an industrial electrician would ask to be honest in the broad context you put it, are you on about a specific size here?.. in answer to your question it depends on a few factors here, the size and type of SWA you require, what its been used for and if the equipotential bonding requirements of the install are been extended through the SWA.

More info is needed here, do you have a copy of the regulations so we can point you in the right direction here?
 
Last edited:
Whether it's as a new installation or an existing one the earthing will generally be achieved by burying a load of metal in the ground and connecting it to the star point.

As far as using the armour as a cpc goes you need to calculate its suitability using the adiabatic equation
 
Your profile gives you as both domestic and Industrial, this is not a question an industrial electrician would ask to be honest in the broad context you put it, are you on about a specific size here?.. in answer to your question it depends on a few factors here, the size and type of SWA you require, what its been used for and if the equipotential bonding requirements of the install are been extended through the SWA.

More info is needed here, do you have a copy of the regulations so we can point you in the right direction here?[/QUOTE

yes I have a copy
 
Hi Mr Darkwood
i want to know what the regulations state about Armour earthing over all..... or could some one direct me to the correct paragraph in the regs. That explain armour Earthing and bonding ....I have my own regs copy.

As I understand it is a forum for Questions so I don't see what my profile have to do with the Question .

Many thanks

enjoy your day

regards
 
Hi Mr Darkwood
i want to know what the regulations state about Armour earthing over all..... or could some one direct me to the correct paragraph in the regs. That explain armour Earthing and bonding ....I have my own regs copy.

As I understand it is a forum for Questions so I don't see what my profile have to do with the Question .

Many thanks

enjoy your day

regards
for most application the armour of SWA up tp 95mm is adequate as a cpc. it might not be adequate for a bonding conductor.
 
Hi Mr Darkwood
i want to know what the regulations state about Armour earthing over all..... or could some one direct me to the correct paragraph in the regs. That explain armour Earthing and bonding ....I have my own regs copy.

As I understand it is a forum for Questions so I don't see what my profile have to do with the Question .

Many thanks

enjoy your day

regards


It wasn't a dig, it was maybe the way you phrased the question and an unusual question to ask from an Industrial Electrician, usually the question is more specific to a size and core number and whether the armour's CSA is adequate, you ask such a broad question it is covered by numerous regulations and subject to application that we cannot just give you a straight answer or guide you to a specific regulation.

If you are asking if the armour can be used as the earth then it can be see (543.2.1), whether you can use the armour as an earth is subject to the specifics of the SWA, the specifics of the use of the SWA (E.G. -If its a submain and equipotential bonding is needed locally then additional earth may be needed).

Whatever you calculate as the requirements and whether the armour meets your needs as an earth or not, its still required to be earthed even if not used as the earth.

There is a table of core count and cable size that shows what cables fall within the CSA requirements to allow for use as a circuit earth conductor I'll try locate a copy for you.
 
Last edited:
Note this is for 70c SWA's thermoplastic

9d70c45e2e8e92df325a7cb84cf1761c


Note - below is for 90c XPLE cables

3b8116624f2f936094d78521c922b42c
 
Thanks so much that's great info .will definitely make good use of it I was not sure about using the armoured in those different ways I know it must be earthed always but now I will study that part of the regs a bit more.

great help

thanks

kind regards
 

Reply to Three phase with neutral....earthing ..? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
816
Hi everyone, this ones a first for me but weve been asked install and use a three phase supply in a large new build house. The 16 way dis board is...
Replies
5
Views
2K
If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
Replies
7
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
261
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock