can someone please tell me why when you change an old rewireable fuseboard to a circuit breaker consumer unit does it have to consist of a time delay rcd on a tt system? and also what would happen if you didn't put a time delay rcd in?
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
W

WarrenG

  • Thread Starter Thread Starter
  • #2
Onsite guide - P24 circuits in a TT system need to be protected by RCD/ RCBO's to protect the circuits.

A 100ma 'S' Type is used as a main switch to protect the whole installation and is delayed for discrimination betwenn the other the RCD's/ RCBO's in the installation.

Hope that makes some sense?

Warren
 

slocm3105

-
Arms
If all circuits are rcd/rcbo protected by a 30mA device, why is there a need to have a 100mA as main switch if others will trip before it?
 
W

wannabesparky

  • Thread Starter Thread Starter
  • #4
what will happen though if a time delay rcd isnt put in?
 
W

WarrenG

  • Thread Starter Thread Starter
  • #5
If all circuits are rcd/rcbo protected by a 30mA device, why is there a need to have a 100mA as main switch if others will trip before it?
This ones been debated before and I think that you are right in saying that if all the circuits are protected by an RCD/RCBO to the 17th Ed then it could be just a main switch. Can't remember now what the conclusion was for it without getting the regs book out.


what will happen though if a time delay rcd isnt put in?
If one of the RCBO's trip then you could have what they call on upstream effect tripping the main RCD out and losing power to the whole installation. Don't forget that the main RCD is a higher rating but looking after the whole installation and not just one circuit.
 
S

Spudnik

  • Thread Starter Thread Starter
  • #6
A standard main switch with RCBO's or dual RCD,s protecting all circuits is permitted on a TT system, providing the CU is either class II or of an all insulated construction.