were would you use a time delay rcd and what are the benefits of doing so is it just in tt installations
Discuss time delay rcds in the UK Electrical Forum area at ElectriciansForums.net
Well use a S Type delayed as the main switch, that's a saving on a main switch, and a 30 Ma RCD on those circuits that require it, which without knowing the job is all of them possibly, I don't want to come across as critical your not insisting on RCD protection on a CU change ? and don't forget also the enclosures type needs to be a class 2 or all insulated for TT's as I interpret the regs
ATB J
I think you misunderstood me. I was not quoting for a CU change. The work asked for was an outside socket off another, RCD protected, CU. I just noticed that the main CU supplying most of the house circuits didn't have any RCD protection and told the guy that wasn't clever. Not suprisingly the guy doesn't want a £100 job turning into a £500 job with CU change so wants the minimum that will give him some protection. That would be an up front 100mA RCD without touching the main CU.
were would you use a time delay rcd and what are the benefits of doing so is it just in tt installations
good point but it does then refer you to 411.1 >415.1.1agricultural and horticultural
705.442.7
Sorry dude got wrong end of stick, just note it on the minor works to cover your ---
ATB J
If you are installing a socket-outlet to be used for mobile equipment outdoors, then the socket-outlet will require 30mA RCD protection.
The problem you have with installing a time delayed up front RCD, is what delay you will use.
1s for distribution circuits, or 0.2s for final circuits?