just been to a quote for new bathroom refurb , new board done, hi integrity crabtree starbreaker CU in place.

TT system

split rcd with 2 ways etc. 30 MA on each, all tested ok.
no time delayed main switch, just standard 100A main switch.
Does this require one as it is split load?
the install is 6 months old?

:confused:
 
Last edited by a moderator:
No, as all circuits have 30mA RCD protection already a 100A 100mA TD RCD is not required.

Unless the CU is metalclad in which case the tails may need additional protection also, as it is a TT system.
 
Not sure what you mean by a time delayed main awitch, are you meaning a S type or time delayed RCD?

On an TT system you would have had a 100mA RCD for lighting etc and then your 30mA for sockets as required on the old 16th. as the new 17th edition now requires that the majority of circuits are now RCD protected this as changed the requirements for TT systems quite a lot.
 
its for a 17th board. This is my first TT board (job) since being registered etc.
Just wanted to double check, i thought that the split dual 30MA rccb's were adequate, but was unsure.
i see alot of 100MA literature banded out about TT systems main switches etc so needed to clarify what im talkin about.
 
the use of the "s" type was to provide discrimination as any fault would take out both the 30 and 100ma rccb's if no time delay was used, now we have 17th edition you would normally just have a main switch and 2 x 30ma rccb's
 

Reply to time delayed main switch? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
279
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
849
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
598
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock