Thanks for your reply. 230v single phase. 3000l tank 3kw run from 16mcbWould need a little more info than you have offered in you query.
What KW is the heating load and are we to presume single phase 230v here and not 3ph?
Thanks for the advice much appreciated.Depends how much you paid for the timer, if its expensive then it is better to have it switching a contactor that then handles the load and takes all the wear and tear of doing so, if you get a 3 pole contactor you have 2 spare poles as back up down the line, if the timer is relatively inexpensive then run the load through the timer as it is rated AC1 16mp and that will be fine for a 3kw load.
You could use the timer to control/operate the contactorLooking for some advice. Can I use a HAGER EH010 timer for the water heater circuit or do I need a contactor.