Hi guys

I've a practical test soon for work as a smart meter installer

Looking for any tips on working with 16/25 stranded singles .Could be a mix of pvc only and sheathed, 7 strand

Im going to make a dummy board and practice moving things around and connecting to improve my profiency

Any techniques for working fast and getting the bends right and the job looking right

TIA
 
Last edited:
strip the cables a little more than you's expect.then when you bend them into position, you find the ends are uneven, so then trim to correct length.
 
and always wriggle and re-tighten terminals once the strands have settled down.
Especially this!!
Local church, several years ago, had a meter change. Installer had tightly twisted the ends of the tails, pushed them into the meter, and tightened the screws. I came along a few days later to add circuits, discovered this, gave the tails a slight anti clockwise twist, and out they all came. Phone call to the DNO wasn't particularly polite.
 
What's the best way to cut straight links and connect them in , do you cut piece slightly long so when it fits in there's a slight bow ?

Also if you're making a link that's straight but has to right angle in at both ends , what's the best way to shape it ? Curve it like a bow ?

Hope the last one makes sense
 
Make it longer than you need : ie have the straight bit as you require but the 2 bits beyond the 90 degree bend make much longer. Then trim/strip accordingly.
The added length will make bending easier. Trying to bend 25mm tails with just a few inches to work with will hurt your hands and fingers.
Should add that given the price of 25mm tails these days dont have too much waste!!
 
Make it longer than you need : ie have the straight bit as you require but the 2 bits beyond the 90 degree bend make much longer. Then trim/strip accordingly.
The added length will make bending easier. Trying to bend 25mm tails with just a few inches to work with will hurt your hands and fingers.
Should add that given the price of 25mm tails these days dont have too much waste!!
In short, do all the bending, before cutting the ends of the tails square.
 
Just remember, you dont want any inner insulation showing when terminating.
What do you mean by that ?

Does the 5mm of inner not show after terminating ?


Do you twist the strands or just push them straight in after cutting, I thought twisting would give a dodgy connection

Or do you twist then terminate and give them a jiggle and retighten?

Bit confused on that one ^ and thanks for all the replies , very helpful
 
What do you mean by that ?
There should not be any primary insulation visible outside of any equipment once the covers, etc, are installed.

So if you have stripped the secondary sheath further back to reveal a sliver of the primary colour (a good idea) then that has to be small enough, copper length not too long, etc, so once all is in place you don't see it outside.
 
Do you twist the strands or just push them straight in after cutting, I thought twisting would give a dodgy connection

Or do you twist then terminate and give them a jiggle and retighten?
You should not need to twist them (really hard to do with 25mm 7-strand anyway), but giving it a good wiggle and re-checking the torque after everything is connected and before the covers finally go on is a very good idea!
 
What do you mean by that ?

Does the 5mm of inner not show after terminating ?


Do you twist the strands or just push them straight in after cutting, I thought twisting would give a dodgy connection

Or do you twist then terminate and give them a jiggle and retighten?

Bit confused on that one ^ and thanks for all the replies , very helpful
The reason for the slight step is to prevent copper showing, the terminated cable is pushed right up to both terminal screws, the inner insulation goes up the meter terminal holes, so you end up with outer sheathing showing only, hope that makes sense to you cant explain it any other way.
 
Lucien Nunes wanna go camping and fishing sometime , swear wont do your head in if not you telectrix after that dan and Lou for 25 quid
 
do not twist the ends of the tails. also no 90deg. sharp bends. nice raduis bend. when happy then secure tails with a couple of cleats
 
Ok well thanks I'll put all this onto practice

I knew not to twist the strands already

Is it just a knife that's used for stepping back the sheath, do you score it and tear it off
 

Reply to Tips for meter box wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hi everyone, I'm currently working towards getting qualified as an electrician and am hoping to get my foot in the door with an apprenticeship or...
Replies
0
Views
904
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock