At the supply sub station the transformer neutral point is connected to earth via rods. the LV distribution cable has its neutral and earth (lead sheath if applicable) connected at the LV ditribution pillar to the same earth rods. At joints along the length of the supply cable, or every 4th pole on OH supplies, earth rods are used at set distances to tie the neutral to earth (PME). At the customers cutout (PME) a concentric type cable may be used with centre phase and outer neutral connected to the cutout. The customers earth and neutral will come from the same connector block. They are then separated in the customers instalation and must not be combined after this point.
If a paper lead type cable is used and is PME'd then the lead and neutral will be combined often in a henley block. Again the customers neutral and earth will be separated after this point.
If the lead sheath and neutral are not combined it is a TN-S system
 
Last edited:
pmeexplanationuk2.gif
 
you can have PNB n all....Protective Neutral Bonding....like PME but without the earth tappings at regular points as described above by Jason...this is more for single consumer use.......
 
At the supply sub station the transformer neutral point is connected to earth via rods. the LV distribution cable has its neutral and earth (lead sheath if applicable) connected at the LV ditribution pillar to the same earth rods. At joints along the length of the supply cable, or every 4th pole on OH supplies, earth rods are used at set distances to tie the neutral to earth (PME). At the customers cutout (PME) a concentric type cable may be used with centre phase and outer neutral connected to the cutout. The customers earth and neutral will come from the same connector block. They are then separated in the customers instalation and must not be combined after this point.

If a paper lead type cable is used and is PME'd then the lead and neutral will be combined often in a henley block. Again the customers neutral and earth will be separated after this point.
If the lead sheath and neutral are not combined it is a TN-S system

Not where i come from.. Where an old TN-S system PILS cable has been PME'd, the earth bond to the lead sheath is cut off/removed. The N/E connection is provided purely at/from the cut-out. Even the the roded neutral PME'd joints on the main cable string don't incorporate the lead sheath. Not sure what happens at the local Distribution Transformer though!!...
 
Not where i come from.. Where an old TN-S system PILS cable has been PME'd, the earth bond to the lead sheath is cut off/removed. The N/E connection is provided purely at/from the cut-out. Even the the roded neutral PME'd joints on the main cable string don't incorporate the lead sheath. Not sure what happens at the local Distribution Transformer though!!...

Im suprised at that, if the lead sheath to earth connection at the sub became detached or more likely not bonded correctly in a joint, the exposed lead sheath in a customers property could be at a higher potential than earth and be a shock/fire risk. Bonding the lead at PME'd joints and at cutouts keeps everything at the same potential. That said if you get a neutral fault the lead would be carying the neutral current (which would still be preferable to open circut neutral faults on the distribution network)
 

Reply to Tn-c-s how the combined bit works in the Australia area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
I've tried to understand one way or another but this seems to be connected to the DNO fuse/cutout, and then loops down (out of sight) and comes...
Replies
2
Views
732
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
942
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock