Hi. New to the forum. I hope I've chosen the correct category to place my post.
I tested a landlords property recently, turned out to be TNC. I haven't much experience encountering TNC systems. So I've signed up here to pick a few brains.
I'm filling out the report now and keep stumbling on parts due to this type of earthing system.

Bit of info on the property:
Cable enters property into cut-out (60amp) 16mm^2 tails from cut-out to meter, 16mm^2 tails from meter to CU. (No earth as TNC. Do I record the Earthing conductor as 16mm^2?)
Old Wylex board BS5486. Once used re-wireable fuses but now has BS3871 in place.
I then have a 6mm^2 bonding conductor from the Earth-bar in the CU to the Water/Gas

When testing I performed a Zs at the CU., My result 16.3 ohms
I also performed a Zline test at the CU. My result 0.22 ohms & 1.04Ka
Obviously my readings for the Zs are not compliant. I'm questioning myself if I've done it right and how you would test & record the results from a TNC? or would you take the Z Line result? but that's a different test measuring the PFC.

The property also had no supplementary bonding in place, would I be right in thinking due to the system type that it's quite significant? (eg. Code C2)

I'm sure I have more questions to come...
Thanks
 
OP
E
Reaction score
0
At first i thought it was. Couldn't locate an electrode, opened the cover to the CU and only CPC's for circuits + Bonding conductor. The property is a row of council houses, some ex council houses, back to back with each other.
 
OP
E
Reaction score
0
Who would be able to help determine what system has been used? DNO?
Definitely no signs of an Electrode. Each property should have its own electrode right?
Thinking about it, the cut-out they've used would be one you'd find with a TNC-S. Not sure if they use what they've got or use specific types for specific systems. I did perform a test Line to MET and that still returned a reading of 18.8ohms.
 

westward10

Esteemed
Reaction score
19,611
It isn't TN-C as you have separate cpcs and neutrals for your circuits.
It isn't TN-C-S or TN-S as you have no evidence of an earthing conductor from the service head or supply cable however TN-C-S could probably be enabled.
This leaves TT or no earthing system. Where does the "bond" go from the consumer unit.
 
OP
E
Reaction score
0
It isn't TN-C as you have separate cpcs and neutrals for your circuits.
It isn't TN-C-S or TN-S as you have no evidence of an earthing conductor from the service head or supply cable however TN-C-S could probably be enabled.
This leaves TT or no earthing system. Where does the "bond" go from the consumer unit
Would there be anyone (DNO for example) who would be able to confirm what Earthing system has been used?
The bond, annoyingly enough goes under the floor and is attached onto the pipework under the floor. Even though the gas meter is in the house I was able to stick my head under a little hatch and see. However the hatch wasn't big enough for me to get in and get a proper look.

Have you measured Ze at the cut out or CU?
I measured Ze from the CU. Main fuse was tagged, I know it's a bit of a grey area cutting tags & removing main fuses. However it would give me a better insight of what's going on inside the cut out I suppose.
 

DefyG

-
Esteemed
Arms
Reaction score
652
Its possible that you would still get an earth reading (Zs) through parallel earth paths even though the earth electrode is missing.
As #8, would determine if TT or TN-C-S is possible.

Do I record the Earthing conductor as 16mm^2?)
What earthing conductor, I thought you said there wasn't one?
I measured Ze from the CU. Main fuse was tagged, I know it's a bit of a grey area cutting tags & removing main fuses. However it would give me a better insight of what's going on inside the cut out I suppose.

You dont need to remove the main cutout fuse to test Ze
 

timhoward

-
Esteemed
Arms
Reaction score
2,262
The bond, annoyingly enough goes under the floor and is attached onto the pipework under the floor. Even though the gas meter is in the house I was able to stick my head under a little hatch and see. However the hatch wasn't big enough for me to get in and get a proper look.
Get your phone down the hole and take a photo!

A few random questions...
Are you sure there isn't a main earth going straight through the wall behind the CU and down outside in an alleyway to an electrode - I had one like this once and it was quite well hidden.

I have had a couple of rare houses where the water pipe was still used as the earth, which hasn't been allowed for longer than anyone can seem to remember (I asked on here once), but they did have an up front RCD or VOELCB indicating it was designed as TT.

If you have any photo's feel free to post them by the way.
 
OP
E
Reaction score
0
Its possible that you would still get an earth reading (Zs) through parallel earth paths even though the earth electrode is missing.
As #8, would determine if TT or TN-C-S is possible.


What earthing conductor, I thought you said there wasn't one?


You dont need to remove the main cutout fuse to test Ze

No earthing conductor. If TNC was utilised. Would you take the conductor size of the Neutral? (For future reference. Like I say I haven't dealt with any TNC systems)

I did the test at the CU. Didn't remove the main earth (Assumed missing) Incoming Line to Earth bar of CU. Would it be ideal to run the test with the main bond removed?
 

westward10

Esteemed
Reaction score
19,611
If you understand earthing systems you would realise it is not TN-C as this requires a PEN conductor through your circuits, in other words a line and neutral whereby the neutral is the PEN (Protective Earth Neutral). There is no separate cpc and the earth is connected from the neutral through your system. If you cannot verify an earthing conductor either from the head, service cable or electrode you have no valid earthing system.
 
Last edited:

DefyG

-
Esteemed
Arms
Reaction score
652
I did the test at the CU. Didn't remove the main earth (Assumed missing) Incoming Line to Earth bar of CU. Would it be ideal to run the test with the main bond removed?
All earth bonding conductors and cpc's are removed from the earthing conductor (of which you dont have) to test for Ze, so you would have to install an earth electrode to test and/or test to N to determine if TN-C-S is possible. Currently it looks like there isnt't an effective earth (C1)!
 

Reply to TNC Property & filling out EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

F
This is slightly pedantic, so right up my street. I'm filling out an EICR. The sockets are wired in 2.5 (apart from some in the kitchen that have been wired in 1mm 3 core and earth. Don't ask...) with a 30 amp 3036 as ocpd. Forgetting the obvious C2's, the question I have is regarding the...
Replies
6
Views
296
timhoward
timhoward
S
Good Morning all , Carrying out an EICR yesterday on a domestic property TT system , which is not a system I frequently work on. My question is that I have a Plastic CU, All circuits protected by RCBO’s, Satisfactory main protective bonding in place & A Good ZE / PFC well within the limits of a...
Replies
21
Views
940
pc1966
P
V
Hi, I've got to put in an additional consumer unit into quite a large property and rather than daisy chaining them back to a single MCB in the main board which is RCD protected, I wondered if this a better solution: The property is served by TNC-S with an isolator switch. Connect new tails into...
Replies
8
Views
233
Matthewd29
Matthewd29
J
The purpose of this thread is two-fold: to let you folks see an EICR from someone who's too lazy (or busy) to even bother forging his test results. to forward this thread to our letting agents after it receives some replies; hopefully, after they've read the opinions of some qualified sparks...
Replies
13
Views
717
Pretty Mouth
Pretty Mouth
1Justin
I've come across a DNO installed (SSEN) 3 Ph 3 core PNE supply cable from a private substation to a large Lucy domestic head. Cable 3 Ph is copper "armoured" (or is there a better name for it?). Entirely underground, entirely within a domestic single owner property. No obvious practical or...
Replies
15
Views
388
R

Electrical News from Electricians Forums and Friends

E
  • Article
Want to become a qualified electrician? Look carefully at the training courses on offer to avoid wasting time and money, is the advice in a new campaign from electrical industry body The Electrotechnical Skills Partnership (TESP). With thousands of searches each year on terms such as...
Replies
49
Views
6K
Marty92
Dan
  • Article
You can now link your account with social media by going to the following page. https://www.electriciansforums.net/account/connected-accounts/ We had this feature some time ago but I removed it when Facebook was found to be selling the data they collected without informing the users of what...
Replies
0
Views
2K
Dan
Dan
  • Article
There was a dodgy advert, typical clickbait, showing "how to save 90% on your electricity bill" which was not the case and it was actually showing some dangerous wiring tactics. Read the actual threads here:- What should be the code for this - C2 or C3 -...
Replies
37
Views
8K
Jurassic Sparks
Jurassic Sparks
James
  • Article
The Go Plus hot tub is being recalled because you could get electrocuted taking a dip, according to press releases from the Chartered Trading Standards Institute (CTSI). An Amazon spokesperson said: "Safety is a top priority at Amazon. "We require all products offered in our store to comply...
Replies
6
Views
3K
Dave Appleby
D
Dan
  • Article
Posted on behalf of @CKI:C.K-Tools Carl Kammerling International Ltd, also known to as ‘CKI’, are the company behind the C.K Tools brand. Founded in Germany in 1904 and with roots stretching back to 1790, we provide a wide range of hand tools, tool storage, power tool accessories and...
Replies
2
Views
4K
telectrix
telectrix

New Posts (Please Reply)

Search Forum

Top