Took a look at a block of flats today that has a TNC-S supply. Each flat is fed by a 2-core mineral insulated cable. The earth and neutral are then combined again using a henley block prior to entering the consumer unit. Has anyone come across this before?
 
Interesting. I can see why it might be done and that is could be considered safe, assuming the Ryfield board is TN-C-S, but I don't know where the line on ESQCR prohibition of TN-C use is drawn as far as (possible) BNO operations are concerned.

MICC is fantastic stuff, but the high CCC is achieved by running the conductors hot as the 'MI' part can safely and reliably do that, so often VD is the limiting factor on an otherwise unremarkable length. Perhaps it was upgrading flats from historic 40A to modern 60A and someone realised that using the outer copper CPC in parallel with the N conductor would achieve acceptable VD and CCC dissipation limits?

As far as safety is concerned, I see it very unlikely that both the outer CPC and the neutral conductor could become disconnected to present a risk. However, that is still not really dealing with the specific limits on ESQCR & wiring regs on TN-C use.
 
Last edited:
Interesting. I can see why it might be done and that is could be considered safe, assuming the Ryfield board is TN-C-S, but I don't know where the line on ESQCR prohibition of TN-C use is drawn as far as (possible) BNO operations are concerned.

MICC is fantastic stuff, but the high CCC is achieved by running the conductors hot as the 'MI' part can safely and reliably do that, so often VD is the limiting factor on an otherwise unremarkable length. Perhaps it was upgrading flats from historic 40A to modern 60A and someone realised that using the outer copper CPC in parallel with the N conductor would achieve acceptable VD and CCC dissipation limits?

As far as safety is concerned, I see it very unlikely that both the outer CPC and the neutral conductor could become disconnected to present a risk. However, that is still not really dealing with the specific limits on ESQCR & wiring regs on TN-C use.

ESQCR regulation 8 only dictates that a customer may not combine the functions of a live conductor and earth in a single conductor.

It doesn't prevent two seperate conductors being connected together (though I think it should), and it only talks about the "customer" - essentially predating BNOs etc.

I would expect the interconnection of N & E to be prohibited in the connection agreement with the DNO/supplier.

It also breaches 543.4.3 of course.
 
ESQCR regulation 8 only dictates that a customer may not combine the functions of a live conductor and earth in a single conductor.
Ah, an interesting and important distinction between having a a PEN conductor and more generic TN-C
It doesn't prevent two separate conductors being connected together (though I think it should), and it only talks about the "customer" - essentially predating BNOs etc.

I would expect the interconnection of N & E to be prohibited in the connection agreement with the DNO/supplier.
Would be interesting to know when, why, and by whom the linking was done.
It also breaches 543.4.3 of course.
Presumably then the BNO side is under the wiring regs rules and not DNO rules?
 
Can you show the other end of those cables.
Unfortunatly I don't have a photo with the trunking off but this is what was going on:

The MICC is terminated onto metal trunking via a gland. The trunking then had a bolt going through it with a 16mm2 earth fly lead into the consumer unit and another into the henley block containing the incoming neutral.

The main supply prior to the Ryefield is TNC-S.

So the question is... what to put on the EICR?

Screenshot 2022-05-04 at 23.37.52.png
 

Reply to TNC-S Supply but combined again at DB? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
504
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
665
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
696

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock