Hi all, I am doing work atm in a block of flat were they have added on extra flats and I doing all the isolators and meter tails. The dno have supplied a 3 phase PME cutout. I am wondering in regards to the earthing connections if the dno will supply an earth bar or if it is up to myself to install this and also if there are any regulations as to what type of earth block/bar is required.
 
Hi all, I am doing work atm in a block of flat were they have added on extra flats and I doing all the isolators and meter tails. The dno have supplied a 3 phase PME cutout. I am wondering in regards to the earthing connections if the dno will supply an earth bar or if it is up to myself to install this and also if there are any regulations as to what type of earth block/bar is required.
The requirements for a switchboard including earthing bar (MET) are detailed in ENA TS37-4.

However, who supplies this is within the agreement between the DNO and Customer.

It depends on the size of the installation, for smaller installations the DNO would just provide a cut-out, the metering the meter and after which you may split into sub meters etc. In this case it would generally be the end customer providing everything other than meter and cut out.

Again in the larger sizes the customer would generally provide a full switchboard, the DNO the cut out, and metering ALL the meters.

However in-between there are times when the DNO provides the board, splitting into many MPANS , other time the customer provides this board or functionality etc.

Most times, if you provide the board, you are responsible for the MET.
 
Has this become a BNO environment? In which case it will almost certainly fall to the owner not the DNO. You don't say what size the incomer is but a 400A earth bar with link isn't expensive (although they can be a pain to find space for!!)
 

Reply to TNCS - Earthing connections in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
493
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
729
Looks very strange to me. Obviously had a new fuse carrier fitted to it at one point but the two cables on the left go to the meter as normal...
Replies
3
Views
680
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock