Hi just checking the main protective bonding conductor size on a tns system, there are two supplys the tails sizes are both (630x2 the supply earth is 240 and neutral is 630x1) persupply
designer aspecified main erthing conductorto met fothe main protective bonding as 2 x 240 i think this i overkill andthe lad on site have installedthis andare putting 50mm forall bonding i think it should be 25mm but looking at table 5.1 in guidence note 8 the table only goes upto 400mm tails
therfore wat size conductor to a: The met forthe bonding, b: The met to the pipework,steel etc
i thnk only nees 25mm
 
SO long as you are sure it is TNS earthing arrangement then the main equipotential bonding does not normally need to be above 25mm².
However if it may be TCNS then 50mm² should be OK.
If you have a designers specification then it would be wise to check why they have specified 2x240mm² as you would be liable for the cost of changing it if there is a cogent reason.
this would seem to be an indication of a TCNS system with a dubious neutral connection!!
 
its is 100% an tns system, there are two supplys to the lv panel,630mm per phase then a single 630mm for the neutral, and a seperat 240mm single as the earth,, both earths on the supply tag onto the integral earth bar inside the panel, then off the earthbar,, designer has said 2x240mm onto our earth bar for the bonding, then iv said thers no need it should have been only 25mm to feed the earthbar then 25mm to rest of things to be bonded am I not right??
 
its is 100% an tns system, there are two supplys to the lv panel,2x630mm per phase then a single 630mm for the neutral, and a seperat 240mm single as the earth all of tis again for othr supply
,, both earths on the supply tag onto the integral earth bar inside the panel, then off the earthbar,, designer has said 2x240mm onto our earth bar for the bonding, then iv said thers no need it should have been only 25mm to feed the earthbar then 25mm to rest of things to be bonded am I not right??
 
its is 100% an tns system, there are two supplys to the lv panel,2x630mm per phase then a single 630mm for the neutral, and a seperat 240mm single as the earth all of tis again for othr supply
,, both earths on the supply tag onto the integral earth bar inside the panel, then off the earthbar,, designer has said 2x240mm onto our earth bar for the bonding, then iv said thers no need it should have been only 25mm to feed the earthbar then 25mm to rest of things to be bonded am I not right??

Had a few beers this afternoon so forgive me if I sound a bit dense, 2x630? don't understand
 
well im there testing it so need to advise them otherwise but hardwork sometimes, people don't want to listen, can anything increase the size of the main protective bonding conductors exept the resistance of the cable in the point your trying to bond is a fair distance away
 
If the main protective bonding conductors are also being used as circuit protective conductors for a remote power supply then the conductor must meet both csa requirements for earthing and bonding.
 
Why are you questioning the designers? They have designed the installation and accept the liability for that design.
So what if you think it is over specced? There could be many reasons for this, especially in an environment with a lot of high tech equipment like that.
Where does the main bond for the lightning protection and structural steel terminate? These may well need to be a lot bigger than 25mm.
 

Reply to Tns main protective bonding conductor csa in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
664
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Just double checking please - in situations where the main earthing conductor csa is calculated, and in a TNS installation, the 50% bonding...
Replies
4
Views
1K
EICR recently done, Swa sub mains armouring used for cpc & MEBPC. Installed 40 years ago, water/gas/structural bonding required, these are @ 10mm...
Replies
31
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock