EDF have requested a building be converted to a TT system.

Currently a TNS 2x100a head supplies a shop then a flat respectively.

The are x2 fuse boards supplying the two areas each having 30ma RCD protection on all final circuits.

Am I correct in saying in simple terms X1 earth spike Into ground, separate the TNS - TT earthing systems from each other and x2 200ma time delay main RCD switches on the two supplies on the meter tails for each supply.
 
Why are EDF requesting this? They are not a licensed DNO in the UK so it's none of their business.
[automerge]1575625380[/automerge]
Am I correct in saying in simple terms X1 earth spike Into ground, separate the TNS - TT earthing systems from each other and x2 200ma time delay main RCD switches on the two supplies on the meter tails for each supply.

No, you need as many earth rods as is necessary to create a stable and reliable earth connection. The chances of 'X1 spike' satisfying this requirement are slim to none.

As you have two seperate installations you need to consider how the earthing systems of the two installations will interact.
Assuming you need to link the earthing systems of the two installations you need to ensure that an alteration to one installation won't have a detrimental effect on the other one. e.g. If someone carries out an EICR on one installation and disconnects the earthing conductor to carry out testing will this leave the shop installation live without an earth?

If you install one set of earth electrodes to serve both installations who will own and be responsible for maintaining the earth electrode network if it is shared by two installations?

If you install seperate sets of earth electrodes for both installations will you need to, or be able to, physically seperate them?
 
Last edited:
As above I don't get this. Are they asking to TT both installations or just the new converted part.
 
We can begin from the beginning...what readings were obtained,from the origin?
What has anyone been instructed,to do with the existing earth arrangements?
 
there Is only one supply for both parts of the building so only need one TT rod, the head splits bits is one supply still

The number of supplies does not dictate the number of rods, the type and condition of the soil dictates the number of rods.

What do you mean by the head splits? If there two meters and two installations connected to the same head then that is still two installations.
 

Reply to TNS - to TT conversion in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock