Hi guys, Am doing a industrial job that will be using 32Amp three phase welders, there is not a masive budget on this job but common sense tells me to use Mem excel isolators due to the breaking currents but do you think I could get away with rotaries instead to keep the cost down or are they all cheaply made and a no go for this type of equipment.
Reason i ask is all will be on 3p&E sockets anyway, job has quite a few supplies i'm running and wanted to keep it uniform but the cost is knocking it up higher than i wanted. was just after your thoughts. cheers.
 
Bearing in mind when the switch is opened it will see a back EMF from the welder the switch needs be suitably rated for breaking inductive loads ie AC 3
 
Cheers for your input guys, all much as i thought just needed a prod.
Thanks Paul I was aware of PUWER but TBH I thought it was general H&S stuff but not read it all as got bored when i had it mentioned some time back, from your comment I best read it through in case points are relevant to this.

I have not done many welders in the past, perhaps a couple of small ones years ago from memory so thought better gen up a bit, One I remember was two phase, which I understand is quite common. These are three phase and balanced as far as I know and running off the same sub-board so any tips I should take heed of would be good. If not pre-wired I was looking at SY as on plug, can you see any issues with that. cheers.

Edit
Did not say whoops, will be three or four on same DB.
 

Reply to To Mem or not ? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
138
Welcome to Accelleo! We are excited to present an excellent opportunity for Electronic Engineers to work within the Security and Defence space...
Replies
0
Views
2K
Posted from another forum "Pretty easy to spot exactly what type of client you're talking too once you've met and dealt with several, and I used...
Replies
2
Views
987
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock