Hi,

As I mentioned last night, I was going to be putting the earth rods in for this summer house this morning.

I put 8 rods in, this was one stack of two, and two stacks of three rods.

The readings from the two that were 3 rods deep were around 10 Ohms per location, and the two rod stack was approx 17 Ohms.

I tested the first rod at approx 10 Ohms, then connected the second rod to the first which was 17 Ohms which them reduced the total down to approx 6 Ohms, then connected the third rod which was 3 deep and that bought it down to 3.2 Ohms.

So the Ra that I achieved today was a respectable 3.2 Ohms

All rods were connected together with 16mm earth.

I am going to go back next week and bang in another couple of piles of two rods so another four in total because I want to get that sub 1 Ohm reading.

Anyway, what do you think, 3.2 is not bad is it!!


Reading from first rod: 10.6 Ohms (3x 4ft 5/8" Rods)
2015-05-15 10.13.58.jpg

Reading from second rod: 17.2 Ohms (2x 4ft 5/8" Rods)
2015-05-15 10.13.12.jpg

Reading from third rod: 9.6 Ohms (3x 4ft 5/8" Rods)
2015-05-15 10.09.17.jpg

Reading from first and second rod combined: 6.3 Ohms
2015-05-15 11.09.49.jpg

Reading from all three rods connected together: 3.2 Ohms
2015-05-15 11.56.56.jpg
 
Hi,

As I mentioned last night, I was going to be putting the earth rods in for this summer house this morning.

I put 8 rods in, this was one stack of two, and two stacks of three rods.

The readings from the two that were 3 rods deep were around 10 Ohms per location, and the two rod stack was approx 17 Ohms.

I tested the first rod at approx 10 Ohms, then connected the second rod to the first which was 17 Ohms which them reduced the total down to approx 6 Ohms, then connected the third rod which was 3 deep and that bought it down to 3.2 Ohms.

So the Ra that I achieved today was a respectable 3.2 Ohms

All rods were connected together with 16mm earth.

I am going to go back next week and bang in another couple of piles of two rods so another four in total because I want to get that sub 1 Ohm reading.

Anyway, what do you think, 3.2 is not bad is it!!


Reading from first rod: 10.6 Ohms (3x 4ft 5/8" Rods)
View attachment 29132

Reading from second rod: 17.2 Ohms (2x 4ft 5/8" Rods)
View attachment 29134

Reading from third rod: 9.6 Ohms (3x 4ft 5/8" Rods)
View attachment 29133

Reading from first and second rod combined: 6.3 Ohms
View attachment 29135

Reading from all three rods connected together: 3.2 Ohms
View attachment 29131


Good work. Bet you only get down to 1.5 ohms with the next rods driven in mate....sods law I think we call it! You could always put any RFCs on a 20A and tell them they can't use their electric shower and hob!! Tell them disconnection times are very very important!! Look forward to the update mate.

Neil
 
No a load of rubbish, pull them all out and start again!!:mad2::53:

I would say 3.2Ω is a pretty good reading, 71A fault current enough to trip a 10A MCB.
Pretty close to the resistors in parallel results actually which is interesting to know.
Thanks for putting in the effort to give us some feedback.
 
I think I'll put two more locations in and end it there, I bet each will knock an ohm off the figure.

it about killed me off beating them in with a lump hammer!

By the time the group has settled the reading will have got better as its really only the bottom rods that are in are touching the earth as the others are flapping round due to the couplers.
 
The first one was easy, the second was a little touch, but the third rod was the killer, the deeper you go, it just gets sodding hard work.

I need to achieve a higher fault current really as 71A is pants, just looking at the time current tables in the BYB and max zs etc.
 
I applaud your efforts with this one I really do. Looks like you will end up with something close to very good.

I have to say though, driving coupled rods with a lump hammer..... don't you like yourself very much ?
 
I think I'll put two more locations in and end it there, I bet each will knock an ohm off the figure.

it about killed me off beating them in with a lump hammer!....
You must be mad, get an attachment for a jackhammer. Also if you want a better Ra go 1 rod deeper on all your existing locations rather than making new locations.

By the time the group has settled the reading will have got better as its really only the bottom rods that are in are touching the earth as the others are flapping round due to the couplers.[/QUOTE]
 
Im not going to get a 0.2s disconnection with 71A, so need to improve that some what!

How many amps am i going to need to get 0.2s ? I know its RCD protected but thats not the point!
 
You must be mad, get an attachment for a jackhammer. Also if you want a better Ra go 1 rod deeper on all your existing locations rather than making new locations.

By the time the group has settled the reading will have got better as its really only the bottom rods that are in are touching the earth as the others are flapping round due to the couplers.
[/QUOTE]

I could try putting another on the top of them, I could do with someone holding the rod so i can hold the hammer with two hands.
 
I could try putting another on the top of them, I could do with someone holding the rod so i can hold the hammer with two hands.[/QUOTE]

or one of these :D much easier

[video=youtube;vvCZvNj8H30]https://www.youtube.com/watch?v=vvCZvNj8H30[/video]
 
Last edited:
I could try putting another on the top of them, I could do with someone holding the rod so i can hold the hammer with two hands.[/QUOTE]


you tried something like this? might help

[video=youtube;0sLv4LLVPbA]https://www.youtube.com/watch?v=0sLv4LLVPbA[/video]
 
I'd need an SDS max bit wouldn't I? and I could rent a drill to do it, presumably an SDS max drill would do it or would I need something bigger?

thats fine, prob normal sds would do but might take longer, but vid below is sds max demolition hammer

[video=youtube;VJYhHZYu_4g]https://www.youtube.com/watch?v=VJYhHZYu_4g[/video]
 
i just get glennsparks to come round and snarl at the rod. the rod then drives itself in.:uhoh2:
 

Reply to Todays Earth Rod Efforts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
968
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
972
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Short version: does code specify a minimum distance from the panel to the first grounding rod, and if so, what is that distance? Long version...
Replies
1
Views
575
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock