Discuss toilet ceiling light in the Lighting Forum area at ElectriciansForums.net

Lynda@972

DIY
Reaction score
2
Hi,
I am trying to change my toilet ceiling light, the old one is just a standard light fitting...but has six wires 2 red, 2 black, 2 earth...light fitting.jpg

My new fitting only has 3 fitting holes light fitting 3.jpg I tried fitting the new one...putting the same wires together in each hole...the light came on but the switch was in off position when i turn it on the tripped the lecky...any ideas where i put all these wires in three holes...
 
The two reds need connecting together and kept separate, do not connect to new light. The black which was connected to the brown at the old light to L, the black connected to the blue at the old light to N and the earths to the middle terminal.
 
If you still had the original connections as per your first photograph, you would have needed to replace the 2 wire white flex containing the blue and brown with a short length of 3 core flex, the brown and blue of which should be connected in the exact terminals as the original, and the green/yellow into the bare screw terminal with the green/yellow sleeving on the wire; the other end of this flex should go to your new fitting, Brown to L (Live/Line), Blue to N (Neutral), and green/yellow to E (Earth).

Unfortunately, now you have removed these connections, this is no longer possible and you would need to re-create the above:
The two red wires would need to be connected together (and to nothing else other than a connector/terminal block)
The two CPC ( the bare un-insulated wires in the middle of the cable) need to be connected together and also connected to the E (Earth) terminal on your new fitting.

One of the black wires would be the neutral wire and needs to be connected to the N (neutral) terminal on your new fitting.
The other black wires would be the Switched line wire and needs to be connected to the L (Live/Line) terminal on your new fitting.

The polarity of these last two is going to be quite important, but now they have been disconnected it is impossible to tell which one is which without a sequence of dead/live tests.

I recommend you now get an electrician to fix this for you as it is beyond simple DIY to identify the correct connections
 
Can you show a pic of the wires as they are now as the neutral does appear to be a single conductor.
 
If you still had the original connections as per your first photograph, you would have needed to replace the 2 wire white flex containing the blue and brown with a short length of 3 core flex, the brown and blue of which should be connected in the exact terminals as the original, and the green/yellow into the bare screw terminal with the green/yellow sleeving on the wire; the other end of this flex should go to your new fitting, Brown to L (Live/Line), Blue to N (Neutral), and green/yellow to E (Earth).

Unfortunately, now you have removed these connections, this is no longer possible and you would need to re-create the above:
The two red wires would need to be connected together (and to nothing else other than a connector/terminal block)
The two CPC ( the bare un-insulated wires in the middle of the cable) need to be connected together and also connected to the E (Earth) terminal on your new fitting.

One of the black wires would be the neutral wire and needs to be connected to the N (neutral) terminal on your new fitting.
The other black wires would be the Switched line wire and needs to be connected to the L (Live/Line) terminal on your new fitting.

The polarity of these last two is going to be quite important, but now they have been disconnected it is impossible to tell which one is which without a sequence of dead/live tests.

I recommend you now get an electrician to fix this for you as it is beyond simple DIY to identify the correct connections
I have put the old light back in and it works fine....i am waiting on an electrician coming Tuesday to fit new light as i dont have a dead/live testing tool...Thanks for your help...
 

Reply to toilet ceiling light in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I have 2 lights connected to 1 switch. I installed a led light fixture on one light, it had one red wire and one black wires. It was easy to match...
Replies
0
Views
251
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi all, how easy is it to be able to shorten the drop tube of a semi flush light fitting ? Essentially what tools would I need for cutting the...
Replies
6
Views
513
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
634
Hello everyone, hope all are well. I'm changing a ceiling rose and have lost the diagram showing where everything was connected (to the old light)...
Replies
8
Views
876

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock