They do when a lost neutral is the problem. If more wires than should be are 'live', then that's likely to be the clue to follow.You may be able to pick up lives with a pen, or non contact detector, but they don’t work on the neutral side.
All doWhat did you test for power with? If it's one of those pens that lights up then it could be giving a false live reading by picking up induced current from elsewhere. Do any other lights on the same breaker work?
Only live on the return - we put everything back as it was before & no light at all.They do when a lost neutral is the problem. If more wires than should be are 'live', then that's likely to be the clue to follow.
You may be able to pick up lives with a pen, or non contact detector, but they don’t work on the neutral side.
A photo of the fitting will help… if it’s one of those badly designed decorative things, the connectors will be too small, the casing has no space, and there’s nowhere for the earth wire to go…
Done all of that, tested both light fittings with a plugIs it possible the old and new lights don't work for two different reasons?
I guess you've tried to eliminate the possibility of faulty bulb, and faulty new fitting, eg by putting a plug on the new light to check it works?
With screw-in bulbs, depending on design of bulb and holder, I've occasionally had the outer bulb contact (at the bottom of the holder) failing to connect with the bulb thread, even with the bulb screwed in tightly. The remedy can be to bend the contact inwards a bit - with the power off obviously!️
Posted a picture of the connections at lighting point alreadyWe need to see the connections at the lighting point.
I thought this too, now how the hell do I find it??? From the room above, under the floorboards?I take it that your last pic. is the supply to the old light?
In that case, you don't have the usual problem when we get these threads of nine or more wires to sort at the lamp, but it does tell us (from the green sleeving), that the wiring is fairly old, and that the connections between the switch, supply and lamp cables are elsewhere, probably in a junction box.
It's very possible that in disturbing the cable you've pulled a wire from an already loose terminal in that junction box.
No thing has been done construction wise to that area of the house. What we did was take down the original light fitting/ bulb, wired up the new pendant light & then nothing. Checked power is going to all wires light switch end and ceiling light end - there is. Even hard wired the old light fitting up (I know I know) - still nothing. All other downstairs lights work fine.The joint box is usually on the landing, just at the top of the stairs…. But as above, you’ll need to lift carpets and boards to find it.
It will be a square or rectangle plastic box with all the grey twin and earth cables running into it.
It would be unlikely that the fault was here… but not impossible.
I would spend more time checking the connections at the switch and light fitting before pulling up boards.
Has there been any construction work where the cable might have been damaged?
I know the sort of box you mean, but I associate these with earlier wiring, often VR. I think I've even seen them used with lead sheathed, and some with cable clamps as well.The joint box is usually on the landing, just at the top of the stairs…. But as above, you’ll need to lift carpets and boards to find it.
It will be a square or rectangle plastic box with all the grey twin and earth cables running into it.