Perhaps there needs to be several ranges based on cable type , bare , ferruled , bent , multi or single etc
 
Perhaps there needs to be several ranges based on cable type , bare , ferruled , bent , multi or single etc

That won't happen, if pushed on the issue manufacturers will start declaring that terminals are only suitable for one conductor in their instructions.

We'd end up like the USA where they are not allowed to put more than one conductor in a terminal unless the manufacturer specifically states it is OK.
 
Wheel nuts and electrical terminals are different situations.

The torque value for the wheel nuts is set knowing exactly what is being fitted, what its made of etc etc.

Electrical terminals could have a range of types and sizes of conductor put in them, there may even be multiple conductors in there. I can't see how one universal torque setting can be correct for all sizes and types of conductor.
Spot on.

Also wheel nuts are subject to significant forces and vibration making torque settings important. Whereas Domestic Electrical installations are (generally) not subject to these forces & vibrations, and so terminal screws, if nipped up, are highly unlikely to work loose.

I guess the intent to using torque screwdrivers is a catch all to ensure that "nipping up" is done, which explains the vagueness in the regs and manufacturer instructions.

You simply cannot have a universal torque setting that caters for all cable types.
 
Also to mention some electricians torque screwdrivers only range from 1-3 NM like the Wera , which is a bit naff from a £175 tool when some makes of main switches ask for 3.2-3.4NM
 
I think most of the key points have been said.

Terminals should be correctly tightened but the regs don't specify how that is done, however, nobody can argue that using the manufacturer's torque setting is not a good way of doing so and thus meeting the fundamental requirement of a sound connection. To avoid liability then proving you have the tool to do so than comes along.

As an aside, wheel nuts and terminals both have forces making them come apart, in the case of electrical stuff though it is usually thermal cycling and not heavy vibration. What is very different is the general condition of them with terminals generally clean & dry and wheel nut varying a lot in terms of surface condition (rust through to well-greased).

Tightening by torque is not that precise as while the tool may be accurate to a few percent, the thread and fastener head friction can vary a lot depending on its finish (machining / plating quality, etc) and state of lubrication. From memory to around 30% or so. That is why high stress bolts like car cylinder heads, etc, now have other methods of final tightening such as going to a set torque to bed them down and then a given final turn angle so the bolt/stud has a certain degree of elongation and thus preload.

Another approach that is good is to observe the torque versus angle do determine how much yield there is, oddly enough that is basically the traditional craftsman's method found out by years of experience (and often a couple of failures along the way)! More summary here:

Personally I use a torque tool for anything critical, but for small DIN screws, etc, usually just hand feel of experience. I have a VDE screwdriver for doing MCBs, etc, and also a few non-insulated tools left over from DIY on car's etc over my lifetime that get used for the occasional big lug bolts, etc.

In my own very limited experience, Hager, Wylex, and Schneider stuff survived fine at their stated torque, one CPN device started to come apart at the seams so lesson learned - don't use them or take it slightly easier!
 
Spot on.

Also wheel nuts are subject to significant forces and vibration making torque settings important. Whereas Domestic Electrical installations are (generally) not subject to these forces & vibrations, and so terminal screws, if nipped up, are highly unlikely to work loose.

Screw terminals are subject to thermal creep, through which they can become loose, although that's not going to be much of an issue at the time of installation.
 
hmmm....if temperatures are getting high enough to that then cable is likely undersized

Happens at moderate temperatures, especially when stranded cables have been tinned with solder. That is why they shouldn't be tinned.

Doesn't necessarily need such high temperatures for it occur.
 
I think they are mentioned in the regs for fine stranded wires aren't they?
Not exactly, but 526.9.1 says the ends have to be "suitably treated" and ferrules are one way to do that. The other common way is the ultrasonic weld you see on some RCBO neutral tails that are fine-stranded.

Also that section (526.9.2/3) say no to tinning conductors for screw terminals, etc.

Soldering is great though if it is actually the means of connection!
 
Not exactly, but 526.9.1 says the ends have to be "suitably treated" and ferrules are one way to do that. The other common way is the ultrasonic weld you see on some RCBO neutral tails that are fine-stranded.

Also that section (526.9.2/3) say no to tinning conductors for screw terminals, etc.

Soldering is great though if it is actually the means of connection!
Indeed, but who in their right mind gets out the soldering iron station when it takes 2s to put a ferrule on?!
 
In the days before ferrules were widely known outside the panel-building industry, it was quite a popular albeit misguided pastime. For example, we saw a number of small theatre lighting installations with a plug patch at the dimmers, where the flexible patch cords were tinned before connecting to the conduit cables via normal terminal block. Someone obviously tinned their way along the line of them making each and every connection a loose one.
 
As above, was quite common and obviously enough for it to be added to the regs as a no-no.

Ferrules are quite a neat way of helping fine stranded wire, and occasionally I have put them on coarse stranded if it is a big screw terminal instead of cage-clamp, etc, as I have seen wires removed and looking worryingly tin and flat as a result.
 
I'm all for the correct tightness in theory, it winds me up when colleagues use impact drivers to tighten (permanently weld) screw connections in CU's. I'd bet the correct, recommended torque, is less than normal wrist driver tightness.

If it becomes mandatory bureaucracy, how long until you need a calibration certificate for your torque screwdriver.
 
As above, was quite common and obviously enough for it to be added to the regs as a no-no.

Ferrules are quite a neat way of helping fine stranded wire, and occasionally I have put them on coarse stranded if it is a big screw terminal instead of cage-clamp, etc, as I have seen wires removed and looking worryingly tin and flat as a result.
You only have to fix one and then take it out again to see where the screw clamped down and all the strands it missed!
 
I'm all for the correct tightness in theory, it winds me up when colleagues use impact drivers to tighten (permanently weld) screw connections in CU's. I'd bet the correct, recommended torque, is less than normal wrist driver tightness.

If it becomes mandatory bureaucracy, how long until you need a calibration certificate for your torque screwdriver.

You should have it calibrated regularly already.
 

Reply to Torque Talk in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock