I have an existing indoor sauna that hadn't been used for sometime (used plenty before though) and I recently cleared it out and renewed the room its housed in. When switching the sauna on it starts fine for 2 - 3 mins and then trips the RCD switch. So I read online very similar issues but none ideally match my problem. I will give more details below but my basic question is...Is it the Sauna or something else, I'm happy to buy a new one just don't wnat to throw good money away.
The sauna is wired very professionaslly from what I can see. It sits on its own circuit to its own breaker switch with a 35amp fused on and off switch. I've tried isolating the elements (3 of them) and all elements work properly on their own but with 2 or more the breaker trips after a few minutes on. The only thing thats changed since it last worked (other than time as its not been used for about 2 years) is the 35amp fused switch which I changed (I changed it back to the old one and it still tyripped). The Sauna is a dated Harvia Kip60

I'd appreciate any suggestions, as said happy to buy a new one but want to be certain it is the old one thats the issue.
 
Heating elements which have been left idle for a long time can absorb some moisture from the air, this will create a small earth leakage.
If any one element works on its own but when any two are on together it trips then I would suggest that each element has a little damp in it.

If you can safely run each element individually for a couple of hours to get it hot and drive off the damp you should find it then gets back to normal working.
 
Heating elements which have been left idle for a long time can absorb some moisture from the air, this will create a small earth leakage.
If any one element works on its own but when any two are on together it trips then I would suggest that each element has a little damp in it.

If you can safely run each element individually for a couple of hours to get it hot and drive off the damp you should find it then gets back to normal working.
Thats a good idea I'll try that...cheers
 
Heating elements which have been left idle for a long time can absorb some moisture from the air, this will create a small earth leakage.
If any one element works on its own but when any two are on together it trips then I would suggest that each element has a little damp in it.

If you can safely run each element individually for a couple of hours to get it hot and drive off the damp you should find it then gets back to normal working.

Give that man a cigar! I isolated each element as before but as you said I left each one running for an hour or so and then put it all back together and hey presto it works like a dream.

Thank you muchly

Simon
 

Reply to Tripping sauna in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock