Hiya,

Had a Triton T80 8.5Kw shower for the last two years in upstairs bathroom connected to the mains cold supply.

Its still working but cutting out and the water going cold when the upstairs bathroom sink tap is switched on.

Have just bought a new Triton T80 10.5kw shower and hoping this will fix the issue (have the thick wiring connection to fuse box).

But a part of me is wondering if the issue may be with the cold supply being affected in some way and putting a new or more powerful shower is not going to help?

In fact the new 10.5kw shower requires a 1.5bar of water pressure as opposed to 1.0bar for the 8.5kw.

Any pointers? Any way to diagnose if its water pressure or a shower problem?

I guess I could unplug the water connection to the shower box and see what kind of flow is coming out of the pipe? Not sure if there any way to measure if its 1.5br? Just not sure why the shower is working fine, but has started cutting out when the cold sink or bath tap is on and if I am going to make it worse by upgrading the shower? Its about 2.5 years old now and so out of warranty. There is a low pressure warning light on the shower which I have never seen come on.

Welcome any direction please.
 
Last edited:
OP
A
Reaction score
2
common fault. low water pressure. soon as someone flushes the bogtshowers go cold. our whole street is the same. only answer is to feed with pump, but that's not allowed on the mainwater supply. carch 22.
Thanks. Water pressure out of the shower is not good, but the I assume the real test would be to take the cold water supply out of shower and test it to see how fasts its coming out. Maybe this...

How to Test Water Pressure (Expert Guide) - Anchor Pumps - https://www.anchorpumps.com/blog/test-water-pressure-home/

Would have thought the low water pressure light would come on if the shower was cutting out due to lack of pressure.

Just wondering if the water authorities ever slow down the pressure if a tenant hasn't paid a water bill on time, I don't think this happens?
 
OP
A
Reaction score
2
What rating is the cable so that we can
establish with shower. Cause if it a new shower it would be under garrantee.
Its over 2 years so no more guarantee.

Its the really thick cable - at least 10mm and maybe 16mm. When I called Triton they said 10mm min is needed for 10.5kw shower with a 45mA fuse - may have up upgrade the current 40mA fuse.

https://www.tritonshowers.co.uk/media/custom/upload/File-1366041415.pdf

Just don't want the same issues if the probs are with the water supply - checking I am not missing a trick here.
 

brianmoooore

-
Esteemed
Arms
Reaction score
2,030
You are correct in that the higher power shower will make things worse IF all other things are equal.
As mentioned in one of the post above, there should be a filter i the inlet to the shower which may be a partly blocked, so this is the first thing to check.
If all is well there, then this is a plumbing problem, which can almost certainly be improved on, but not necessarily eliminated.
First thing to check is that the main stopcock to the property is turned fully on. It may have been turned partly off to control excessive flow from some taps. The problem taps should then be fitted with their own 'stopcock' (they already should be) which can be turned partly off.
 
OP
A
Reaction score
2
You are correct in that the higher power shower will make things worse IF all other things are equal.
As mentioned in one of the post above, there should be a filter i the inlet to the shower which may be a partly blocked, so this is the first thing to check.
If all is well there, then this is a plumbing problem, which can almost certainly be improved on, but not necessarily eliminated.
First thing to check is that the main stopcock to the property is turned fully on. It may have been turned partly off to control excessive flow from some taps. The problem taps should then be fitted with their own 'stopcock' (they already should be) which can be turned partly off.
Yes, good advice, this is on my radar. Pretty sure inlet its fully open, but will check, downstairs water flow from kitchen tap (near internal stopcock) looks pretty good, but not sure what 1.5 bar looks like and so may have to use the 1litre and timing trick to see (unless there is any other way to do it)?

If the water flow from copper pipe into shower looks good as well, then can only assume the shower or filter need sorting. If flow is good into shower, would prefer a 10.5kw shower as winter months are coming.
 

brianmoooore

-
Esteemed
Arms
Reaction score
2,030
You need to invest in a cheap 4 bar pressure gauge, and a few fittings to enable you to connect it to the shower supply pipe, and see how much the pressure drops at the shower when a tap is switched on.
If it's only the bathroom basin tap causing the problem, a cheap and simple solution would be to lock the bathroom door when using the shower.
 

telectrix

-
Mentor
Esteemed
Arms
Reaction score
65,533
United Utilities tolsme it was the oldleadpipes cominginto the house were furred up and it was our problem. funny thing is...... our mains water comes in t]from the streetmain in copper. proper imperial copper 1/2"pipe, not the new fangled thin walled metric crap that bosts as soon as ot gets cold.
 

Petej999

Arms
Reaction score
164

LastManOnline

Esteemed
Arms
Reaction score
851
Yes, good advice, this is on my radar. Pretty sure inlet its fully open, but will check, downstairs water flow from kitchen tap (near internal stopcock) looks pretty good, but not sure what 1.5 bar looks like and so may have to use the 1litre and timing trick to see (unless there is any other way to do it)?

If the water flow from copper pipe into shower looks good as well, then can only assume the shower or filter need sorting. If flow is good into shower, would prefer a 10.5kw shower as winter months are coming.
Is your bathroom upstairs or downstairs?
 

brianmoooore

-
Esteemed
Arms
Reaction score
2,030
Posted it above. Current fuse thingy-ma-jig says - "32amp MTN 110 6000 Hager fuse" - that OK for a 10.5kw shower?
That sounds like a 32A Hager MCB which is most definitely not suitable for a 10.5kW shower, even if it really is 9.6W. It may not trip during the length of any normal shower session, but will routinely overheat, and suffer internal damage.
It's not even suitable for the existing 8.5kW shower.
 
OP
A
Reaction score
2
You need to invest in a cheap 4 bar pressure gauge, and a few fittings to enable you to connect it to the shower supply pipe, and see how much the pressure drops at the shower when a tap is switched on.
If it's only the bathroom basin tap causing the problem, a cheap and simple solution would be to lock the bathroom door when using the shower.
I actually managed to fit the new 10.5kw shower, not too hard as a like for like replacement. More of a plumbing issue as tried to use the same olive with the water supply and it leaked everywhere. New 15mm nut and olive later and it was water tight.

I did check the water supply before fitting to the shower - it was mains pressure and came gushing out so I assume it made the min 1.5 bar Triton requirement for this shower.

But even with new 10.5kw shower fitted, the same issue happened with the bathroom tap. When the bathroom tap is fully on, the electric shower goes cold with no "low pressure" light coming on. Tried going downstairs and leaving the kitchen tap fully on and that didn't effect the upstairs shower. So I assume the shower cold is probably T-ed of the sink tap and it effects the shower more (just miffed why the low pressure warning light isn't coming on the shower when it cuts out).
 

brianmoooore

-
Esteemed
Arms
Reaction score
2,030
The water coming from the shower should momentarily go hotter before cutting out, and I would certainly expect the low pressure light to come on.
In most houses, the kitchen sink tap is much closer to the incoming main than the bathroom, so perhaps the kitchen tap already has a partly shut off valve connected before it. Does the bathroom basin tap have an isolator valve, as it should have? If so, try turning this partly off, to restrict the basin flow a bit.
Are you using the shower head supplied with the shower? Electric showers use a far more restrictive head, in terms of flow, compared to that used with 'proper' showers, to create sufficient back pressure in the shower to operate the flow switch.
 
OP
A
Reaction score
2
That sounds like a 32A Hager MCB which is most definitely not suitable for a 10.5kW shower, even if it really is 9.6W. It may not trip during the length of any normal shower session, but will routinely overheat, and suffer internal damage.
It's not even suitable for the existing 8.5kW shower.
Oh ok - do I need a Hager 145 45A fuse thingy then? Maybe like this, but its looks a bit odd shapped?

Else this one is 50A and assume it will do the job?

Not sure if changing the cartridge is reasonable things for non elecy to do (I don't want to die). Seems reasonably straightforward? Anything to be careful off? - aka the main tail ends from the supply will always be live?


 
OP
A
Reaction score
2
The water coming from the shower should momentarily go hotter before cutting out, and I would certainly expect the low pressure light to come on.
In most houses, the kitchen sink tap is much closer to the incoming main than the bathroom, so perhaps the kitchen tap already has a partly shut off valve connected before it. Does the bathroom basin tap have an isolator valve, as it should have? If so, try turning this partly off, to restrict the basin flow a bit.
Are you using the shower head supplied with the shower? Electric showers use a far more restrictive head, in terms of flow, compared to that used with 'proper' showers, to create sufficient back pressure in the shower to operate the flow switch.
Ah OK. Will try the shower head and isolator valve adjustment.
 
OP
A
Reaction score
2
The water coming from the shower should momentarily go hotter before cutting out, and I would certainly expect the low pressure light to come on.
In most houses, the kitchen sink tap is much closer to the incoming main than the bathroom, so perhaps the kitchen tap already has a partly shut off valve connected before it. Does the bathroom basin tap have an isolator valve, as it should have? If so, try turning this partly off, to restrict the basin flow a bit.
Are you using the shower head supplied with the shower? Electric showers use a far more restrictive head, in terms of flow, compared to that used with 'proper' showers, to create sufficient back pressure in the shower to operate the flow switch.

Adjusted the Isolator value on the cold into the Bathroom sink and it did the job. Turned it just enough so even max output on the tap did not cause the shower to go cold. Thanks for that. ;-)

Surprised the Triton shower low pressure light did not come on if there was an issue with the water inlet into the shower unit.
 

telectrix

-
Mentor
Esteemed
Arms
Reaction score
65,533
Then you have convenient access to your attic and the obvious and desirable option is a pumped shower. You get better and trouble free flow. Need never again worry about a toilet been flushed or a tap been turned on. And you are unaffected by mains pressure variations. A pumped shower is the ideal way to go
then advise here. have a pumped shower off C/H. hot is pumped, cold not. when shower tap is on cool, it's freezig. soon as turn tap to activate pump, it's scalding. no regulation.
 

Zerax

-
Esteemed
Arms
Reaction score
1,483
A mate of mine had is loft converted.. which meant getting rid of the cold water storage tanks (CWS) in the loft and installing a mains fed hot water storage tank. Then they built a massive new housing development across the road...

Now he has pressure issues (but pressure is above the legal minimum)... that would be solved by re-installing the CWS tank into his daughters bedroom !
 

Reply to Triton T80 Easi-Fit Shower Cutting out with sink tap on ;-( in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Dartlec
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom above - and got a shock from the bathroom tap (and his 'pen glowed on everything') Turned up to check and, sure enough, voltage of 16V AC showing on the...
Replies
22
Views
645
captaincaveman
captaincaveman
B
Hi All, I wondered if someone might advise me on an issue I am having. I turned off my power to replace a plug socket in my house and when I turned the power back on, the burglar alarm started going off. Unfortunately I have just bought and moved into the house and I do not know the codes...
Replies
8
Views
384
Strima
U
Good afternoon guys, I was wondreing if anyone could help with the issue I have at home. I have a MIRA offset quadrant shower (built around 3/4 years ago approx), and I am having leakings (see attached the photos). I have tried to put some silicone several times but the water is still going...
Replies
6
Views
676
polaroid
P
J
Hi guys I have been asked to fit new shower and run new cable for it too, looking at regs book it would have to be reference method 103, which for 8.5kw shower would mean 16mm cable, can terminals in the shower take 16mm and the terminals in the isolator? I have tried looking for different cable...
Replies
25
Views
2K
LastManOnline
L
F
I just went to replace a 45A pullcord for someone as it had stopped working. It's only been in a year so I assume it must have been a loose connection during installation as a couple of the connections, particularly neutrals, were very loose in the switch but fine at the board and in the shower...
Replies
6
Views
628
telectrix
telectrix

Electrical News from Electricians Forums and Friends

E
  • Article
Want to become a qualified electrician? Look carefully at the training courses on offer to avoid wasting time and money, is the advice in a new campaign from electrical industry body The Electrotechnical Skills Partnership (TESP). With thousands of searches each year on terms such as...
Replies
49
Views
6K
Marty92
Dan
  • Article
You can now link your account with social media by going to the following page. https://www.electriciansforums.net/account/connected-accounts/ We had this feature some time ago but I removed it when Facebook was found to be selling the data they collected without informing the users of what...
Replies
0
Views
2K
Dan
Dan
  • Article
There was a dodgy advert, typical clickbait, showing "how to save 90% on your electricity bill" which was not the case and it was actually showing some dangerous wiring tactics. Read the actual threads here:- What should be the code for this - C2 or C3 -...
Replies
37
Views
8K
Jurassic Sparks
Jurassic Sparks
James
  • Article
The Go Plus hot tub is being recalled because you could get electrocuted taking a dip, according to press releases from the Chartered Trading Standards Institute (CTSI). An Amazon spokesperson said: "Safety is a top priority at Amazon. "We require all products offered in our store to comply...
Replies
6
Views
3K
Dave Appleby
D
Dan
  • Article
Posted on behalf of @CKI:C.K-Tools Carl Kammerling International Ltd, also known to as ‘CKI’, are the company behind the C.K Tools brand. Founded in Germany in 1904 and with roots stretching back to 1790, we provide a wide range of hand tools, tool storage, power tool accessories and...
Replies
2
Views
4K
telectrix
telectrix

Search Forum

Top